I think your getting a bit confused and hung up on what the manual is telling you. It is referring to the cold water inlet, which has strainer inside the iso valve (15mm cold inlet) and a filter inside the flow switch. And not related to your problem.
What I'm telling you to do isnt listed in the Baxi manual.
Turn the power off
Isolate the boiler using the CH iso valves far left and far right.
Drain the boiler of heating water.
Look at the far right 22mm heating return valve
Put a spanner on the largest of the front facing nuts and undo it. Not the one above connecting to the brass body.
Once removed you will see a tubular strainer similar to that you found in the cold water inlet valve.
Have fun