Radiators warm up nicely then.....

Joined
21 Jun 2011
Messages
109
Reaction score
7
Country
United Kingdom
Throughout house then suddenly the 2 in the front large kitchen/diner will go cold
My Honeywell thermostat control unit is in the back room and because it’s a cold room with high ceilings I’ve set it at 25c
All the rads have those thermostatic controls and all are working and not stuck
The rads have been bled and all were fine
When i tinker on the rads control very slightly the rad will warm up again! Please tell me what is going on or point me in a direction where I can maybe do trial and error or anything
Also I want to service my Magnaclean pro 2( I do it every year) but this time I can’t turn the top lid with the special large spanner, it seems to be stuck fast and I done really want to remove the whole unit as that seems hard too, if I use real force I might bend or cause a leak issue from the adjoining pipes ..... any suggestions guys
Thanks in advance
 
Sponsored Links

CBW

Joined
26 Sep 2019
Messages
11,644
Reaction score
3,254
Location
North
Country
United Kingdom
All rads have trv’s? Including the room thermostat one?
 

CBW

Joined
26 Sep 2019
Messages
11,644
Reaction score
3,254
Location
North
Country
United Kingdom
You could try bleeding the magnaclean to release this. As for the rads, try turning all other valves off, leaving the 2 problematic ones, see if they heat up. Sounds like it just need balancing.
 
Joined
21 Jun 2011
Messages
109
Reaction score
7
Country
United Kingdom
Ok will try that, also the shower room radiator towel rad ( it’s probably the nearest to the boiler... just) is boiling hot even when the thermostat is on lowest setting ....
 

Attachments

  • 41684389-22C5-47D7-AFDC-5E18A5128CAF.jpeg
    41684389-22C5-47D7-AFDC-5E18A5128CAF.jpeg
    218.4 KB · Views: 50
Joined
27 Feb 2017
Messages
22,108
Reaction score
2,284
Location
Essexshire
Country
United Kingdom
Remove the TRV head from the one in the room with the thermostat. You shouldn’t have a TRV in that room.
 
Sponsored Links

CBW

Joined
26 Sep 2019
Messages
11,644
Reaction score
3,254
Location
North
Country
United Kingdom
Ok will try that, also the shower room radiator towel rad ( it’s probably the nearest to the boiler... just) is boiling hot even when the thermostat is on lowest setting ....
this may not be shutting off correctly then.
 
Joined
21 Jun 2011
Messages
109
Reaction score
7
Country
United Kingdom
Mottie thanks I’ll try that ... any advice on the blistering hot towel rad.?
 
Joined
27 Feb 2017
Messages
22,108
Reaction score
2,284
Location
Essexshire
Country
United Kingdom
Mottie thanks I’ll try that ... any advice on the blistering hot towel rad.?
It’s not a part of the bypass circuit is it? If not, I’m not an expert but if it’s the nearest to the boiler I’d try throttling it right down on the lockshield valve.
 
Joined
21 Jun 2011
Messages
109
Reaction score
7
Country
United Kingdom
Yep I understand that and will give that ago too cheers
 
Joined
20 Mar 2018
Messages
1,480
Reaction score
171
Location
Stoke-on-Trent
Country
United Kingdom
Also I want to service my Magnaclean pro 2( I do it every year) but this time I can’t turn the top lid with the special large spanner, it seems to be stuck fast and I done really want to remove the whole unit as that seems hard too, if I use real force I might bend or cause a leak issue from the adjoining pipes ..... any suggestions guys
Don't let the pipes take the force when you're trying to remove the lid, or you risk damaging them (as you say). Get a mate to hold the body while you use the spanner.
 