Hi guys
Could some one check over my figures please and correct or advise me if I have boobed?
Range Master duel fuel cooker, total electrical load 7.5Kw, which I make about 32.2 Amps
I intend to install a radial supply with 6mm twin & earth of maximum of 8 metres length, a 45amp cooker control switch (without socket) and a 45amp terminal.
Will a 32 amp MCB be ok for this load or should i go up a size? (its that diversity bit I don't really get)
Thanks, Mike