RCD Tripping – Fault Traced to One Socket, Still Trips with Replacement

I'm having an issue with an RCD that keeps tripping as soon as I attempt to turn it back on. I've already unplugged all appliances from the affected circuit, but the RCD still trips immediately. To isolate the fault, I disconnected each socket on the circuit one by one and managed to trace the problem to a single socket.

When this socket is disconnected, the RCD resets without any issue. However, when I install a brand new socket in its place and wire it up, the RCD trips again as soon as I attempt to turn it on.

This suggests the issue might not be the socket itself but potentially a fault in the cable feeding it. There are no obvious signs of damage, but I haven’t carried out any insulation resistance testing yet.

Looking for advice or confirmation from anyone who's seen a similar issue — is it likely to be a neutral-to-earth fault or some other wiring issue in the cable?

I am not an electrician.

In the event that you remove the socket and fit a terminal block, does the fault still exist? I would be inclined to be think that @crystal ball might be correct about a spur that runs off to the outside. I am also mindful of @EFLImpudence point about RCDs and MCBs

Photos will help.
 
Of course, it could be possible that the fault lies within the CU. I've seen all kinds of debris in the back of many over the years.
 
Just to add to the fun, I have found the following causing trips RCD & MCB & fuses,
Slug in JB & TV amp
Suspected melted cable run behind fire place
Water in inaccessible JB, water stain on ceiling below
Water in outdoor kit
Nicked cable in back box
Rodent damage
T&E run outside through a tree, branch had rubbed through
 
that circuit, doesn't have any outdoor sockets, I'm dubious about any water ingress, as we are in a heatwave....
 
The MCB is causing the RCD to trip not preventing it, I will have a look at the wiring coming out of the back box, incase its chaffed....
He means, turning off the MCB is stopping the RCD from tripping. That’s right, isn’t it?
 
that circuit, doesn't have any outdoor sockets, I'm dubious about any water ingress, as we are in a heatwave....
Internal leak maybe, pipework joint failed, I recently re plumbed my central heating, found a dry joint that had held for 40 odd years, could have been a different story
 