Doing a job today and replaced a twin skt using a dual box for two FCUs.
The 13A FCU supplied a 2.5 SWA cable o/s to a w/p box containing a 4-way skt. The 3A FCU supplied 1.5 cable in conduit for two o/s wall lights.
Both circuits went through the wall into a 5-way JB, to keep them separate.
When I did an insulation test for the skt circuit, I got the following results:
L-PE >299MOhms
L-N 245kOhms - I couldn't understand why only 245kOhms!
N-PE >299MOhms
ELI(0.4Ohms) & RCD both ok.
On the other circuit, Insulation tests all >299MOhms
ELI 2.1Ohms
Rcd tests would not trip and showed up as >299ms
I thought afterwards perhaps I should have tried a ramp test, this I can still do. I am using a Megger CM500.
Any ideas or help please?
L-PE >299MOhms
N-PE >299MOhms
ELI 2.1Ohms