Reducing Cable Size

Discussion in 'Electrics UK' started by ryanj, 25 Jul 2005.

  1. ryanj

    ryanj

    Joined:
    5 Oct 2003
    Messages:
    209
    Thanks Received:
    0
    Country:
    United Kingdom
    Having recently run a length of 10mm^2 cable from a 45amp MCB to the cooker control unit, and from there to a cable outlet plate.

    The cable outlet plate will supply the hob.

    I planned on running a further length of 10mm^2 cable from this to an unswitched FCU for the oven supply. But I cannot fit the two 10mm^2 cores into the terminals of the outlet plate.

    Is it okay to reduce the CSA of the cables for the short distance, to perhaps 2.5mm^2 or 4mm^2? (less than 0.25m)
     
  2. Sponsored Links
  3. mapj1

    mapj1

    Joined:
    24 Nov 2004
    Messages:
    1,043
    Thanks Received:
    2
    Country:
    United Kingdom
    If that cable is overload protected by the fuse in the FCU it feeds, and short circuit prtecte by the supply fuse or breaker, then yes, it is acceptable. Not nice, but acceptable.
     