That's exactly it. Don't think just about radiators - think also of things like toothbrush racks, toilet roll holders, hooks, metal door handles, saucepans, spoons - these are all metal items which are not e-c-ps, and connecting them to the cpcs of electrical circuits isn't an increase in safety.This is something I do not understand UNLESS it is that a lump of un-earthed metal ( such as a central heating radiator connected by plastic pipes ) is "safer" as it will not provide a circuit to earth for a person touching both the radiator and a live conductor.
Precisely - the scenario is that there is no chance.That would make sense if there was no chance of the water in the plastic pipes being conductive enough ( inhibitors added, it is not pure water ) to carry a lethal current from the radiator to the earthed / bondded metal work of the boiler.
Such a scenario is not what supplementary equipotential bonding is designed to deal with, and if a fault like that were catered for then what you'd be doing to the radiator would be earthing, not bonding.If any of the metal pipework connected to this radiator becomes live due to being squashed against damaged cables in a shared notch in a joist then the radiator can become live. Holding an earthed metal appliance and touching this radiator would be a potentially lethal shock hazard. In practise the conductivity of the water might be sufficient to trip an RCD when the pipe work and radiator became live but that is not 100% certain to happen.