Is there anything I need to do differently if turning rad valves off and taking a rad off on a vented system as opposed to a sealed? Expect I don't need to open a filling loop after to fill. Thanks
 
Sponsored Links
No, exactly the same just for removal, as in isolate both flow and return valves, and open bleed vent to ensure they’re not passing. Filling up will likely take longer.
 
Worth cleaning out the F&E tank in the loft, because when you refill the radiator it might otherwise allow sludge from the tank into the system.
 