Renegades avanti open vented boiler not starting up

Discussion in 'Plumbing and Central Heating' started by Garry Evans, 12 Feb 2017.

  1. Garry Evans

    Garry Evans

    Joined:
    12 Feb 2017
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,boiler not starting first thing in morning,error 2 code,always starts after reset is pressed and run for rest of day.Gsr has bled system and replaced pump and flow and return stats ,still same fault.Should the pump run prior to boiler ignition,this doesn't always happen.Any help appreciated Garry
     
  2. Sponsored Links
  3. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,575
    Thanks Received:
    1,339
    Location:
    Kent
    Country:
    United Kingdom
    Never heard of a "Renegades avanti" boiler. Can you check this please.
     
  4. Garry Evans

    Garry Evans

    Joined:
    12 Feb 2017
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    Sorry,put this down to predictive text.The boiler is a remeha avanti open vented system
     
  5. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,575
    Thanks Received:
    1,339
    Location:
    Kent
    Country:
    United Kingdom
    Thought it might be a Remeha Avanta.

    To answer your question: yes, the pump should start before the boiler ignites. If it doesn't, the circuit board may be faulty.
     
  6. Steelmasons

    Steelmasons

    Joined:
    10 Oct 2011
    Messages:
    16,404
    Thanks Received:
    3,969
    Country:
    United Kingdom
    :rolleyes:... For an E2 fault??:)
     
  7. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,575
    Thanks Received:
    1,339
    Location:
    Kent
    Country:
    United Kingdom
    one of the reasons give for an E2 in the manual is:

    No through flow: Check that the pump is working; turn the spindle with a screwdriver, if that works but the pump still does not respond, check the wiring;
    that is in order the pump is faulty.


    The OP has said that the pump does not always start before the boiler lights and pressing Reset corrects the problem for the rest of the day. Reset is connected to the PCB so the logical conclusion is that the PCB has an intermittent fault.
     
  8. Sponsored Links
  9. Garry Evans

    Garry Evans

    Joined:
    12 Feb 2017
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks to D Hailsham and Steelmasons for your advice,still can't understand why the boiler will run correctly all day after the reset is pressed.This morning when I pressed the reset I saw that the pump started cycling immediately and a few minutes later the burner lit.
     
  10. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,575
    Thanks Received:
    1,339
    Location:
    Kent
    Country:
    United Kingdom
    It might be worthwhile contacting Baxi Customer Support on 0344 871 1545. They are the official repair company for Remeha boilers.

    Have you checked if your boiler is still in Warranty? Remeha had a habit of changing the length of warranty; but Baxi Customer support should have the info. You will need the serial number - on the plate underneath the boiler.
     
  11. Garry Evans

    Garry Evans

    Joined:
    12 Feb 2017
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,observed boiler throughout day,the boiler ignites the same time as the pump comes on but only occasionally,could it be igniting because the boiler is warm through the day but going to error 2 in the morning when the boiler is stone cold. Garry
     
  12. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,575
    Thanks Received:
    1,339
    Location:
    Kent
    Country:
    United Kingdom
    Not sure what you are saying. Do you mean (a) the boiler comers on occasionally during the day or (b) the pump comes on occasionally?

    When working correctly the pump should come on about one second before the boiler lights.

    igniting? Do you mean the pump starting?

    If so, yes, that is a possibility; if that is happening it suggests a fault with the control system

    Where are your boiler and pump located? Are they in a cold place, e.g the garage?

    The boiler has built-in frost protection as follows:

    - at a water temperature below 7°C: the circulation pump is switched on;
    - at a water temperature below 3°C: the boiler is switched on;
    - when the water temperature is above 10°C: the boiler is switched off and the circulation pump runs for another 15 minutes.
     
  13. Garry Evans

    Garry Evans

    Joined:
    12 Feb 2017
    Messages:
    5
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,yesterday the boiler was repeatedly going to error2,today the boiler has ran ok,the boiler and pump are both in garage,just turned house stat up and observed boiler,burner chamber was cold,both pump and burner came on together.Have noticed other times pump comes on first then boiler fires up a few minutes later.G
     
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page