Thank you for all the responses so far. So I think one of my main concerns at the moment would be changing the unit and then finding additional problems that would result in potentially having to remove wallpaper / freshly painted rooms etc.
Is there any way to check for these faults before swapping the unit over?
Before a fuse board/consumer unit swap, the correct procedure to adopt is an Electrical Installation Condition Report (ECIR)
The report will include:
*A visual inspection of the system/installation. (accessible areas only)
*Dead test: Continuity of earth and live conductors, insulation resistance and dead polarity.
*Live test: Live polarity, Ze (taken at the intake of the installation), Zs (at the furthest point of each circuit), prospective short circuit current (The current which is likely to flow in a circuit if line and neutral cables are short circuited)
RCD test (which it seems you don't have)
*Functional tests: this will generally test the mechanically operation of electrical switches and sockets and safety devices (turning things on/off)
There is a document that is filled out, that will amongst other things, highlight any non-conformities or not to current standards found, these are known as codes.
The codes used to determine whether there are non-compliances or issue with the electrical installation and are numbered C1 to C3. These codes will be entered on the Electrical Installation Condition Report, along with a description of the nature of the fault, and will determine whether a ‘Satisfactory’ or ‘Unsatisfactory’ report will be applied to the installation.
*Code C1 ‘Danger present’: There is a risk of injury and that immediate remedial action is required to remove the dangerous condition.
*Code C2 ‘Potentially dangerous condition’: Urgent remedial action required, this should declare the nature of the problem, not the remedial actions required.
*Code C3 ‘Improvement recommended’ This code more often than not implies that while the installation may not comply with the current set of regulations, complies with a previous set of regulations and so is deemed to be safe although this safety can be improved upon.
All code 1s and 2s must be rectified.
Any code 3s do not, but can be if requested.
One concern with installing an consumer unit with RCD protection to one that did not previously have this protection, is that RCDs are sensitive to earth leakage, which they will detect and if the amount of leakage is enough to activate the RCD, you will have power-loss.
So it is important that this is assessed prior to swap over.
You could also have appliances that are leaking to earth, so you may find yourself replacing or repairing, ovens, microwaves, toasters, irons, kettles, laundry appliances etc...
I very rarely come across an installation where a degree of remedial work is not required prior to a new board being installed, so be aware there will likely be some work required, it maybe that the earth conductor and bonding needs updating which is quite normal, or you could have a fault on the circuit that needs to be investigated, found and corrected (this can be a headache for both installer and occupant)
Inspection, testing and replacing the fuse board is a task that should be undertaken by a competent, qualified person. It will also require notification to building controls.
I hope this post has been helpful?