Hi all,
I’m hoping to get some advice on an issue I’m trying to resolve on the first floor of my house.

The house has been plagued by squeaky floorboards, and as I’m currently renovating one of the rooms, I’d like to address the problem while I have the floor up.

It appears that the existing floor is 18mm chipboard T&G. As you can see in the photo, the stud wall on the left has been built directly on top of the flooring. I suspect this is making the problem worse, as movement/creaks in one room can be transmitted through the floor into the adjacent room.

My proposed solution is to run a plunge saw along the red line shown in the photo, effectively separating the flooring in this room from the flooring in the adjoining rooms. I would then replace the existing chipboard with 18mm plywood.

Does this sound like a sensible approach? Has anyone done something similar, particularly where a stud wall has been built on top of the flooring?

I’m aware that I’d need to provide support underneath all the new board edges, so my plan would be to add noggins where necessary. I’m also considering using larger sheets of plywood rather than T&G boards, to minimise the number of joints and therefore potential points for movement.

Is there anything obvious I’m overlooking? In particular, I’d be interested to hear whether separating the floor in this way is likely to help with the squeaking, or whether there are better ways of tackling it.

Any advice or experience would be much appreciated!

PXL_20260921_154342148.jpg
 
T&G chipboard has to be one of the worst-installed materials in the world - there's nothing wrong with the material per se, and it is easy to install properly - it's just that there are far too many cowboy builders, pricework monkeys, dodgy Bob the Builder types and other assorted idiots (and cheapskates) who can't get their heads round how to select or install the stuff correctly.

The reason why chipboard floors have problems are down to a list of issues:-

1. T&G sheets not glued to tops of joists
2. T&G tongues not adequately glued
3. Boards not pulled up tight when installed
4. Boards nailed down (a pet hate of mine done so frequently by cowboy builders)
5. Or not adequately screwed down (e.g. wrong type of screw, screws too short or too small diameter, insufficient number of screws, screw heads not sunk flush, etc)
6. Screws (or nails) missing joists completely or worse only just catching the edges of joists (which generates squeaks)
7. Sheet not fixed fully down onto joist - there must be not gap under the sheet. If this is a problem for you, drive the screw in, back it out half way they put all your weight on the board and drive again -that normally cures it (but an impact driver really is better)
8. I think that's about all of the boo-boos I can think of, for now...

So depending on how bad your floor is you may be able to just rescrew the entire floor using Floor-Tite screws (or flooring screws if you have an impact driver). Squeaky joints can sometimes be fixed by drilling into the tongue at 45 degrees and squeezing in PU glue - you need to drill every 150mm or so to make this work, but at least you can feel when you hit the hollow where the groove is (about 13mm in at 45 degrees). Maybe worth a try before you start ripping out floors, especially if it is only small areas. I've used a similar repair technique on engineered oak flooring and laminate on a number of occasions, filling the holes with hard repair wax afterwards

One additional issue I have come across is that of a wall sole plate being badly nailed into the joist below it - where the nail has gone in at an angle and either just grazed the joist or only just gone in, causing a split. If plain shank nails are used the problem can be much worse. Those can drive you crazy and may require chunks of plasterboard to be removed to cure 'em (by screwing through the sole plate into the joist, making sure that you don't hit any services which are buried n the ceiling void below)

The reasons for using 8 x 2ft (1200 x 600) T&G chipboard sheets are several-fold: trying to manhandle an 8 x 4ft sheet of anything upstairs is difficult enough (18mm hardwood plywood weighs 35 to 45kg - not good for the back), but getting it round corners/over newel posts and baullustrades, etc can be a bear then trying to position it on bare joists without putting a foot through is beyond some people (ask my last apprentice!). Decent hardwood plywood isn't cheap. either, and you still potentially have the issue of unsupported edges moving (rubbing) - at one time on commercial jobs we used to get the workshop to rout us a 6 x 15mm groove in the edges of 8 x 4 boards and supply 20/22mm wide rips of 6mm plywood which we then glued in as loose tongues. Nowadays we often just use 22mm T&G chipboard or 25mm T&G spruce plywood (which comes in 2400 x 1200 sheets, but is designed for multiple nailed and glued layes, so not suitable for domestic IMHO)

But for anyone interested in how to install T&G chipboard properly, read this:

The procedure requires that you start tongue edge against a wall. If your rows mean that you'll end up with a narrow rip as the last row you may need to take a bit off the tongue edge of the first row before you start laying. Anyway, first mark joist positions along the wall with a pencil. Then run beads of glue (D4 expanding/PU type) along the tops of the joists for only the 2400mm (8ft) length x 550mm or so width of the first T&G sheet you are going to lay - don't go beyond that as you end up covered in glue with black hands. Drop the sheet onto the joists, tongue edge towards the wall and manouevre into position. The chipboard should remain at least 10mm off the masonry - that gap prevents moisture bridging from the walls. The sheet is then screwed down to the joints using flooring screws (4.5 x 45/50mm for 19mm flooring, 4.5 x 60 for 22 or 25mm) at 150mm centres along the joist. You don't need fancy Tongue Tite or Floor Tite screws, but you do need reasonable quality screws, something like single start ones. If it helps use a chalk line (or a straight length of stud and a pencil) to mark the joist positions across the top of the board. These lines need to be in the centre of the joists - accuracy is important. You ideally need an impact driver to do this properly - because most cordless drills simply lack the grunt to sink the screw heads flush unless you laboriously pilot each hole. Run a complete row of T&G before starting the next row, End to end T&G joints also need to be glued as well and pulled up tight. You can align the first row of T&G boards by using a straight piece of 4 x 2in CLS about 8ft long as your straight edge, or a 6ft spirit level (now you know one reason chippies have them ;-) )

The next row needs to be staggered - we call it "brick pattern". For this and subsequent rows run a bead of glue on the top of the tongue, put matching bead along the bottom of the first row groove, and remember the glue beads on the tops of the joists. Don't be stingy with the glue, but also don't flood it. Position the boards touchingeach other then "tap" up tight. By "tap" I mean take a 4 or 5ft length of 4 x 2in CLS and lay it flat against the open edge of the new board, put your heels on the sheet, toes on the CLS, feet widely spaced, then tap the edge of the CLS between your feet with a 7lb sledge hammer. The weight of the sledge means that a few gentle taps is all you need to use to pull the joint up tight, although you may need to move the CLS up and down the sheet a couple of times to even the joint out. If you try smashing the board really hard you run the risk of deforming the sheet's groove edge and the joint may actually open up (equal and opposite reaction - think about the Newton's balls toy). When this next sheet down, mark the joist centres and screw the sheet down as before. And so on and so forth. If you don't have any 4 x 2, 3 x 2in CLS will work - it just that I have big feet...

The glue you use is very important - it MUST be D4 polyurethane (expanding). You only glue and lay a single sheet at a time because (a) this glue goes off fast (so no bunking off for a cuppa before you finish screwing down that last sheet) and (b) if you put too much down you will get it all over your hands, clothes and tools - it makes your skin go black and it takes 2 to 4 days of washing to get rid of it.

The only other thing is don't skimp on the T&G - buy the best you can afford (normally Egger or Caber Decor) and go for a waterproof grade (i.e. P5 - which can be used in bathrooms and kitchens providing the floors are subsequently sealed (e.g. ceramic tiles, welded vinyl, etc)

But I'm saying this as a (now retired) joiner, rather than any other type of trade.... In any case I think I've written quite enough for tonight. G'night
 
Last edited:
It appears that the existing floor is 18mm chipboard T&G. As you can see in the photo, the stud wall on the left has been built directly on top of the flooring. I suspect this is making the problem worse, as movement/creaks in one room can be transmitted through the floor into the adjacent room.

Does this sound like a sensible approach? Has anyone done something similar, particularly where a stud wall has been built on top of the flooring?
I should have answered this before, but I did touch on it in my previous post. Stud walls on upper floors are invartiably built on top of the sub-floor (e.g. chipboard), but in a modern house they should run directly above a joist (or better a doubled-up joist). When a wall creaks it is often just down to incorrect installation of the sub-floor, rather than the wall, so the first thing I'd do is try to fix the floor (extra screws, glue injected into joints, etc).

Only then if you are still having issues will it be worth looking at the wall sole plate. If the wall runs across the joists it should be possible to take the skirting off on both sides and fix the wall down to the joists below using long screws skewed through the plasterboard and sole plate into the joist - just be careful not to hit any services beneath the floor. I'd also consider trying inject some PU glus into the joint between the sole plate and the floor at multiple points

If, however, your wall runs in the same direction as the joists you need to check if it has been properly supported with solid strutting. One way to do this is to drill a 25mm hole through the floor next to the wall at an angle to make an inspection "spy hole". If you have solid strutting (as opposed to, say, 3 x 2s) you can then try the same stitch to the top of the joist trick as before, only you'll be stitching to the solid strutting (on something like 300 to 400mm centres). BTW it may require a few holes to find the strutting, however.

My proposed solution is to run a plunge saw along the red line shown in the photo, effectively separating the flooring in this room from the flooring in the adjoining rooms. I would then replace the existing chipboard with 18mm plywood.

Well, it will work, but floors and joists have a nasty tendency to have bits of ironmongery, etc embedded in them - the older the house, the bigger the issue. Best get yourself some cheap blades in case you miss taking a nail or screw out which will then find and wreck your blade. Also be prepared to deal with kickbacks - in other words don't kneel directly behind the saw, instead work to one side.

Frankly, though, I'd try fixing the issue in situ first if I could, and only resort to ripping the floor out if you can't fix it. The technique I've quoted for laying a chipboard floor is bulletproof, and is what based on what manufacturer's like Egger recommend. Properly installed T&G chip doesn't creak - the problem is some of the muppets who think they know how to install it...

Advice based on about 5 decades as a carpenter and joiner, so I have dealt with issues like this before far, far too many times for my liking.
 
Thank you very much for the extremely comprehensive reply, I will read it a few times and make sure I understand it all! All the potential fixes you have suggested I have unfortunately tries so I will be pulling up the floor.

So you would suggest that maybe I don't need to go for plywood T&G? It is quite expensive but at this point I don't care if it costs twice as much if it makes squeaks less likely.

Thanks again for the reply, I'll be using all this information as a guide throughout the process.
Thanks
Lee
 
So you would suggest that maybe I don't need to go for plywood T&G? It is quite expensive but at this point I don't care if it costs twice as much if it makes squeaks less likely.
Cost is one reason for using chipboard, the fact that plywood has plain edges (which can move sgainst each other unless you take steps to stop it), and the complete PIA that is manhandling 8 x 4ft sheets if plywood is a third.

Surprised you'd tried all the stuff I mentioned - even glue injection? That's a useful fix for squeaky laminate or engineered flooring (and refilling holes with coloured hard wax filler)
 
Chipboard is awful stuff and I did the same.

18mm will fit straight in without a step, but, as well as putting all the joints on top of joists, add struts "noggjns" under all cut edges. Otherwise there will be a small amount of flex when you walk on them.

You can screw them down, which will be useful if you ever need access. This is a good time to add a floor safe, or a hatch to the void.

You can paint or varnish for improved cleanability and water resistance. I used hardwood faced ply, and dyed and varnished it before fitting (including the edges) in bathroom and kitchen.

On the ground floor, consider packing between tge joists with mineral wool to block draughts and reduce heat loss.

On other floors it will slightly reduce airborne noise transmission, but the heavyweight batts are more effective for noise muffling.
 
Last edited:
Thanks for the reply, so I don't need noggins on T & G joints? I was basically going to add noggins all around each board so no edge, even if its joined via T&G would be left unsupported. Have I gone abit over the top with that?
 
I've had floors relying on the T&G, and I say, add a strut and screw both pieces down.

They fail first in high traffic areas, like in front of the sink, at doorways, and at the bottom of the stairs where people step (or jump) off.
 
(I am no professional, just a householder enraged by shoddy floors)
 
(I am no professional, just a householder enraged by shoddy floors)
And someone who doesn't know how to install chipboard flooring correctly? ;-) You always seem to confuse poor installation with poor quality materials, and come up with the same advice every time.

As with laying ANY sub-floor, you need to ensure that the services beneath it are in good condition - so no lead-clad, brown paper insulated electrical wiring, no lead piping, no corroded copper wiring and most importantly NO (and I mean NOOOOO!) push fit or compression fit wastes. In other words it all needs to be in good order. That way you'll probably never need to unscrew a sheet of anything - although unscrewing a sheet is often not a viable approach, at least not if you have a glued LVT floor, a welded vinyl floor, a laminate floor or even (sometimes) a fitted carpet. Also screwed-down sub-floors can still suffer from squeaks - which is why any competent joiner glues [i[and[/i] screws sub-flooring in place - and is why we use T&G flooring (or failing that loose tongues, glued in place). My feeling is that if you need to be able to lift a floor a T&G planked softwood floor will be a better solution and with the price of plywood there isn't that much difference in the cost of the materials, however installation does take longer, and just as with T&G chipboard you do need to know what you are doing. At least you don't need to lug full-size sheets of 8 x 4ft plywood around.

Personally, I like the way they route services in countries like Italy, where it all gets put through conduit, so that when you come to rewire or replumb, much of the services can just be pulled through the conduit. Byat that's another story entirely
 
And someone who doesn't know how to install chipboard flooring correctly

I was only ever trained to lay pine boards.

Since then, I have only worked on floors installed by others, mostly unsatisfactory.

I don't need to know how to install chipboard flooring, since I never do it.

Of course I speak as I find,
 
Paint onto the bare boards, the routes of all services and label.
When I did my 2x bedrooms, ensuite and landing, I noggined all board ends at the correct level plus, infilled any low joists with timber slithers. The whole lot is as solid as a rock, no squeaks and level. We've porcelain-tiled the ensuite floor. Quite a ball-ache at the time but, 14 years later, all still sound.
 
I have nothing to add to @GhostIntMachine 's sage advice but I would say that I have never seen microbore rad pipes run through a blanking plate with a flex hole. Is that normal?
 
I replaced all the boards with 22mm chipboard and there is basically no improvement... I didn't bother gluing down as I could tell the floorboards are not the issue, the joists are the things that are creaking. Standing on the joists directly with no boards still creaked. Could I try sistering the joists perhaps?
 