At one point, electricians would design a circuit, not just do it that way, as that's the way we have always done it.
So I was given a job, a large fridge for storing cheese, you could have fitted at least two of my houses inside the fridge, it was large, with fork lifts running around inside it.
It needed cleaning, so they wanted a load of 13 amp sockets, so the cleaners could be plugged in, the walls were around 20 foot high, so to run a ring final in a conventual method, the drop to each socket would be 35 foot, so we used 6 mm² junction box to junction box, with 2.5 mm² drops to each socket, every socket was a radial from a junction box, which the diagram

permits shown about 11 o'clock. The volt drop was not quite within limits, centre of ring, we swapped some of the drops to using 4 mm² we had not actually calculated it all first, but the scrubbers etc, were not that dependent on voltage, so it did not matter too much.
With another job we did get caught out on volt drop, it seems shrink wrap machines do not like volt drop, but domestic wise, very little will have a problem with volt drop, if within the current limits to work the magnetic part of the MCB.