You've been advised incorrectly by the inspector - not that he should be advising at all; his job is to inspect what's been specified.
There seems to be a reasonable width of wall between the door and French window, so the new beam could easily sit on the 100mm inner skin. There would be a spreader-type padstone, the length of which would be calculated depending on the type of blockwork.
Windposts are only required if lateral stability is an issue, and 9 times out of 10 it isn't. In your case, it could probably be proved that the width of wall
is OK and the load from upstairs will provide stability. The floor joists seem to span parallel to the wall, so 3 or 4 straps between the underside of the joists and the wall would not go amiss.
If the beam is supported solely on the steel column, and there is cracking upstairs, then the foundation of the steel post has settled.
There seems to be a reasonable width of wall between the door and French window, so the new beam could easily sit on the 100mm inner skin. There would be a spreader-type padstone, the length of which would be calculated depending on the type of blockwork.
Windposts are only required if lateral stability is an issue, and 9 times out of 10 it isn't. In your case, it could probably be proved that the width of wall
is OK and the load from upstairs will provide stability. The floor joists seem to span parallel to the wall, so 3 or 4 straps between the underside of the joists and the wall would not go amiss.
If the beam is supported solely on the steel column, and there is cracking upstairs, then the foundation of the steel post has settled.