saunier duval 623

Joined
20 May 2006
Messages
229
Reaction score
13
Location
Essex
Country
United Kingdom
hi have this boiler no hot water or heating.the pilot is alight and fan running ,pressure is 1.5 bar.Pressure switch is making switch ,could yo please advise how to test to see if gas valve has power going to it.There are two wires going to the solnoid on gas valve ,could any one help with any other advice to get this boiler going thanks peter
 
Sponsored Links
multimeter?, are you getting volage on one of the wires at least?
 
hi ollski what is the best way to test,is one side of multi go to earth and other to terminal or a prope to each terminal.How old are these boilers thanks peter
 
One test point on gas valve live, other on common neutral at wiring block.
 
Sponsored Links
It could be the high limit stat.

Top left of heat exchanger (violet spot i believe they call the sensor).
 