Hi i gave a saunier duval sd30e combi boiler. I bled the radiators yesterday and have got home to a low water pressure light flashing on my boiler and the pressure gauge showing 0- any ideas
 
Sponsored Links
topping the pressure up with the filling loop. would be a good start.
 
if that means opening the valve with the black handle i have tried that
 
see if the filling loop that you tried, which will have a braded hose.attached.has a screw driver slot on one of the valves.try turning that.usually though most filling loops have a handle at each end.hence the sugestion of the slotted valve.
 
Sponsored Links
thanks, despite being a girl i have got some sense and had figured needed to fiddle with valves however have moved thoses at both ends, independantly and together but to no joy am guessing that maybe there is a reset switch or somthing somewhere????
 
close the valves

remove silver pipe

point it into a bucket and tutn on valve

do you get water out

being female is not an excuse btw :LOL: ;)
 