can anybody help?? everything works except bell box when alarm is activated. key pad test for internal & external sounder works but when alarm is activated only internal sounder works. its a texecom bell box with led's flashing left to right as should be. linked panel to test that strobe & sounder works...fine!! whats the problem? replace panel?
 
Sponsored Links
more info please.

is this a new external siren, is it the old one, why have you changed it, has anything else been done?

also have you checked the voltage on the bell trigger terminal? it should be 12v -ve when in alarm or bell test
 
In a FULL ALARM CONDITION do you have 12v between BELL (Neg - signal) & 12v (Pos - Hold Off) at the sounder connections inside your control panel?

That will tell you if it is the Sounder or the Panel is at fault, lets not worry about cable faults yet, try the basics.

Basically, fully set your alarm and go outside, let it set correctly, come back in, Entry timer starts, walk into any area that is NOT on your entry route, should then get an instant alarm. DON'T TURN IT OFF.

Open the control panel and with your multi meter do as I've indicated above.

If you have no meter or are not happy doing this, 240v Mains Electricity in the control panel, find an engineer who will be able to sort it out
 
Sponsored Links
As europlex says , you need to set off a FULL alarm , my guess is you are not letting the 2-ply entry tones finish.

EG. 15 sec entry tones , 15 secs internal alarm , then external siren starts.
 