Oh I see what you mean, it was 2009 however maybe he has re-trained now? Because at one point my job for 6 months was installing earth rods and measuring their impedance I am fully aware of how to install an earth rod, both from scratch and using the DNO supply as a reference point. But having read some PIR and EICR and seem the reading given it is clear other electricians don't seem to know what they are doing.
When I see a TT installation with a Ze of 10Ω or less it rings alarm bells. Not saying you can't get a Ze of 10Ω but in the main I find water and gas pipes were left connected when measured. The external loop impedance to my mind should be the electrically permitted earth connection and not any part which could be removed by non electrical personal. So should not include any connection to gas or water pipes, but could include connection to re-bar in the building foundations.
To measure the Ze below 50Ω really does need the two test probe method. To compare to the DNO supply we have to remember they are only required to have a 15Ω earth so with a reading of 200Ω the 15Ω is not really a problem, but to get a reading of 8Ω unless you know the DNO reading then the two electrode method is the only option. However although with the gas terminus I was working on one can get the distance required, with a domestic getting electrodes in the ground to measure the earth rod is often impossible.
As to if we should record the Ze as <XΩ where we use the DNO as a reference point is debatable.
However when I was at collage I have to admit I was not shown how to measure Ze until I did my C&G2391. By that time I had used the earth rod measuring kit as I had needed to install earth mats for galvanic protection, so came out of my time 1972 but it was 1980 before I had to measure earth mats. Do remember at that time collage qualifications were not required to be classed as an electrician.
So although clearly bad that some one who should know how to fit rods does not, however it is really a reflection on the scheme providers that they can accept people who clearly have not been trained.
The question must be, is there any point in the scheme providers if they don't test electricians to find their skill level? However no one has zero potential, even when I did the job for 6 months I sill did not have zero potential even if that was the standing joke.