Set up Texecom Premier Elite 48 so Internal sounder goes 1st

Discussion in 'Alarms, CCTV & Telephones' started by SgtWilson1, 31 Dec 2014.

  1. SgtWilson1

    SgtWilson1

    Joined:
    31 Dec 2014
    Messages:
    50
    Thanks Received:
    0
    Location:
    Hertfordshire
    Country:
    United Kingdom
    I have currently wired the panel with the Outside Bell Box coming off the bell outputs on the board. I have the internal Picollo coming from -OP1 and to +12V.
    Everything is fine but on alarm they both sound at the same time. I would prefer to have only the internal on first. Is there a way of delaying the outside bell to come on 1 minute later?

    I have wintex software and a laptop connection to the panel. I've stabbed around in Global delay and RKP delay but no joy so far.
     
  2. Sponsored Links
  3. sparkymarka

    sparkymarka

    Joined:
    16 Feb 2011
    Messages:
    8,806
    Thanks Received:
    1,342
    Location:
    Sheffield
    Country:
    United Kingdom
    Make op1 alarm not bell set bell delay to 1 min in areas
     
    • Thanks Thanks x 1
  4. SgtWilson1

    SgtWilson1

    Joined:
    31 Dec 2014
    Messages:
    50
    Thanks Received:
    0
    Location:
    Hertfordshire
    Country:
    United Kingdom
    You Superstar sparkymarka. Sorted -thank you. Happy New Year to you :D
     
  5. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page