Several sockets and lights on a spur?

Joined
24 Nov 2013
Messages
396
Reaction score
18
Location
Berkshire
Country
United Kingdom
Hello All

2.5mm ring is protected by a 32a rcbo in the main consumer unit.

I'm thinking about using a short length of 4mm to spur from a socket into the garage which is on the other side of the wall. This would feed a small "garage" consumer unit with a (I think pointless from a protection point of view) 40a or 63a main breaker switch. From there would be a single 2.5mm radial on a 16a mcb and another 1.5mm radial lighting on a 6a mcb.

Is that allowed or does the whole lot need to be on a 13a fused spur or does it all need to come direct from the main consumer unit ?
 
The 40 or 63A "main breaker switch" is just a double pole switch offering no protection at all.
 
Electrically and regs wise there is nothing to stop you putting a consumer unit on a ring, it does offer an advantage of total isolation of the garage if required. I would suggest using nothing bigger than 16A MCB's or RCBO's.
It would be nicerer to extend the ring to the new CU with 2 cables to match the existing ring rather than use a 4mm² spur.
 
Extend the ring and you have options to break into it again later if the need arises.
 
Extend the ring and you have options to break into it again later if the need arises.
So why can you not do that with a 4mm² spur (or radial)?

There is no point having a ring circuit with both legs in the same place.
 
But is such a spur allowed ?
2.5mm ring is protected by a 32a rcbo in the main consumer unit.

I'm thinking about using a short length of 4mm to spur from a socket into the garage which is on the other side of the wall. This would feed a small "garage" consumer unit with a (I think pointless from a protection point of view) 40a or 63a main breaker switch. From there would be a single 2.5mm radial on a 16a mcb and another 1.5mm radial lighting on a 6a mcb.

Is that allowed or does the whole lot need to be on a 13a fused spur or does it all need to come direct from the main consumer unit ?
If you use 4mm² for the whole spur no fusing is necessary and you can have many sockets.
 
Either way you could run the sockets straight off of your new connection and the lights off an FCU with a 5 A fuse.
 