Basins do not have zones. Fixed baths and showers have zones. https://www.google.com/url?sa=t&rct...00002375.pdf&usg=AOvVaw1Pv2d0vrjJ4sX4kPMGCHoD
"Note 2
A shaver supply unit must be to BS EN 61558-2-5 (701.512.3). The requirement
for a degree of protection of a minimum of IPX4 in zone 2 does not apply to
shaver units situated where direct spray from showers is unlikely (701.512.2)."
1) They have to be over 600mm from the edge of the bath.
No, because "Note 2
A shaver supply unit must be to BS EN 61558-2-5 (701.512.3). The requirement
for a degree of protection of a minimum of IPX4 in zone 2 does not apply to
shaver units situated where direct spray from showers is unlikely (701.512.2)."
2) Is there no measurement given for a basin and shaver.
No, because basins do not have zones.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local