It looks as if you may have done ....
If it looks that way to you then your seeing is faulty.


What aspect of "seem" and "seemingly" do you think indicates certainty?
How about the fact that they do?

upload_2018-1-12_1-8-49.png

upload_2018-1-12_1-13-7.png
 
Sponsored Links
John said "it would seem". Does that denote certainty?
Yes.

]...but 522.6.204 allows that cable while only calling for an earthed metal covering. It does not mention screen.
A difficulty not helped (again) by sloppy language in the Regulations.


Do you therefore agree a covering is a sheath - and vice versa?
What I agree with is that these terms are not properly defined or consistently used in BS 7671.

What I agree with is the idea that they might be defined in other standards.

What I agree with is that no matter what usage you point to in BS 7671, BS 8436 clearly does not define the screen in those cables as the sheath, and clearly does not define the sheath as that screen, or covering over the cores.

What I agree with is that there is nowhere near enough clarity for you and John to be justified in your conclusion about what is suitable for direct burying.

What I agree with is that you are still trying to argue yourself out of accepting that there is nowhere near enough clarity.


It may be unsuitable underground for different reasons but 522.8.10 only calls for an earthed metal sheath.
And as we can see, nowhere does BS 8436 say that it has one of those.


Is a screen also not a covering and so the cable should not be suitable for burying in walls?
I have already referred to sloppy language in the Regulations, and how unhelpful it is, so I don't think there is any point in trying to analyse it. These terms are not properly defined or consistently used in BS 7671, so you're not going to be able to use them to arrive at any firm conclusions.


Is the armour (of swa) not a sheath and so not suitable for underground?
That question makes no sense - armour and sheath are two different things, and a cable does not have to have both.

522.8.10 ... a cable buried in the ground shall incorporate an earthed armour or ...
 
This is how IDH describe their Guardian cable:
  • Plain annealed stranded copper conductor to BS6360
  • XLPE insulation to BS6889
  • Aluminium screen tube, applies longitudinally.
  • ...
So there is a continuous aluminium covering, a "tube", enveloping part of the cable ?
In the absence of any contradictory definition (see the dictionary definitions I quoted earlier in the thread), this is therefore "a" sheath - being a covering on a cable. It's primary function may well be for EMC screening, but unless you can find a definition of sheath that excludes an "aluminium tube enclosing the cores" then that cable would appear to meet the requirements in BS7671 IF the CSA of the tube is sufficient to be used as a CPC for the circuit.
As said, there may be other reasons not to bury it, though having XLPE insulation suggests that the non-waterproof nature of PVC isn't one of them, but the lack of a metallic sheath isn't one of them.

I trust you aren't arguing that a cable can only have a single "sheath" ?
 
Sponsored Links
I trust you aren't arguing that a cable can only have a single "sheath" ?
I trust you aren't arguing that a cable for which the standard does not say it has a metal sheath but does say it has a plastic sheath can be considered to officially have a metal sheath?
 
No, I'm arguing that a cable that has something which meets the dictionary definition of "a sheath", and where that "sheath" is metallic, has something which is a "metallic sheath" regardless of what the manufacturer or standards call it.
So are you arguing that aluminium is not metallic ?
Are you arguing that a "tube" enclosing the cores does not meet the definition of "sheath" ?

Because unless you argue that one of those is incorrect, then it is rather hard to see how you can argue that in the case in question, the cable does not have "a" metallic sheath. It also has an XLPE sheath over the top of that, but that doesn't alter the nature of the sheath inside it.

Unless you have found some official definition of sheath that differs from what everyone (except, it would seem*, you) accepts as being a "sheath". If you have, then post a link and we can all stand corrected - but until you find and post such a definition, then we have to assume that you are being belligerent in your usual manner of having your own definitions and trying to claim that the rest of the world is wrong.
* Yes, using the dictionary definitions I recently posted showing it's use as "would appear" :whistle:
 
No, I'm arguing that a cable that has something which meets the dictionary definition of "a sheath", and where that "sheath" is metallic, has something which is a "metallic sheath" regardless of what the manufacturer or standards call it.
You may not take a term defined by a standard, give it a different meaning, and then claim that the standard says that the {whatever} has that thing.

So are you arguing that aluminium is not metallic ?
Are you arguing that a "tube" enclosing the cores does not meet the definition of "sheath" ?
I'm arguing that the definition of the construction of a cable to BS 8436 does not give it a metal sheath.


Because unless you argue that one of those is incorrect, then it is rather hard to see how you can argue that in the case in question, the cable does not have "a" metallic sheath.
I can point out that in the definition of how a cable to BS 8436 shall be constructed, it is not given a metal sheath.


It also has an XLPE sheath over the top of that, but that doesn't alter the nature of the sheath inside it.
There is no sheath inside it.

If there is, please show us in BS 8436 where that sheath is defined. For the avoidance of any doubt, the standard must refer to that component as a sheath, for if it does not then it clearly is not a sheath as far as the standard is concerned.


Unless you have found some official definition of sheath that differs from what everyone (except, it would seem*, you) accepts as being a "sheath". If you have, then post a link and we can all stand corrected - but until you find and post such a definition, then we have to assume that you are being belligerent in your usual manner of having your own definitions and trying to claim that the rest of the world is wrong.
* Yes, using the dictionary definitions I recently posted showing it's use as "would appear" :whistle:
I'll add you to the list of people whose only concern seems to be to argue themselves out of accepting that there is clearly insufficient clarity about the term for any claim that there is to be valid.

You say I have my own definitions, but you are demonstrably using a definition which contradicts what the BS for that type of cable says.
 

upload_2018-1-12_13-6-38.png



What I agree with is that these terms are not properly defined or consistently used in BS 7671.
Therefore all we need to consider is covering and sheath.

What I agree with is the idea that they might be defined in other standards.
They might be. Are they?

What I agree with is that no matter what usage you point to in BS 7671, BS 8436 clearly does not define the screen in those cables as the sheath, and clearly does not define the sheath as that screen, or covering over the cores.
Does it have to define covering for us to know that the screen covers and as such may even be a sheath.

What I agree with is that there is nowhere near enough clarity for you and John to be justified in your conclusion about what is suitable for direct burying.
We have not conclude that. We are discussing the possibility with you.

What I agree with is that you are still trying to argue yourself out of accepting that there is nowhere near enough clarity.
Surely a lack of clarity increases the possibility.

I have already referred to sloppy language in the Regulations, and how unhelpful it is, so I don't think there is any point in trying to analyse it. These terms are not properly defined or consistently used in BS 7671, so you're not going to be able to use them to arrive at any firm conclusions.
Can we not therefore rely on standard English definitions.

upload_2018-1-12_13-0-46.png


upload_2018-1-12_13-3-4.png


It depends who you ask:

upload_2018-1-12_13-12-36.png




That question makes no sense - armour and sheath are two different things, and a cable does not have to have both.
It does not, but to be buried in the ground a cable may just have a metal sheath.

522.8.10 ... a cable buried in the ground shall incorporate an earthed armour or ...
Accepted. Sorry, I had forgotten that in all the discussion.[/QUOTE]
 
Try looking in a Dictionary rather than a Thesaurus ;) VERB 1 Give the impression of being something or having a particular quality. And Collins seem to agree as well - to appear to the mind ..., to give the impression ...
Indeed.

Furthermore, I don't really care what definitions can be found in dictionaries or any thesaurus. When I add the word "seem" or "seemingly" into a sentence (let alone three times into the same sentence), I do so deliberately in order to indicate a lack of certainty. Virtually everyone will understand that such is my meaning/intention, and most of them will use the words in the same way for the same purpose themselves. If a dictionary or thesaurus indicates otherwise, I would say that it is the dictionary/thesaurus which is 'wrong' in terms of how our language is used.

Consider "The answer to the question seems to be .....". Would anyone (other than BAS) take that to mean the same as "The answer to the question certainly is ...."?

Kind Regards, John
 
As far as regulations are concerned, I don't think one has to look any further than 522.8.10. That seems to indicate very clearly that any cable with an earthed metal sheath may be directly buried, provided only that that sheath was "suitable for use as a protective conductor" (does that just mean adequate CSA, or what, I wonder?). [other regs obviously require that the cable be suitable for the environment concerned, but without saying anything specific].

However, I still wonder what responses somewhat would get if they came to this forum and said that the wanted to directly bury something other than SWA!
How about "522.8.10 only seems to indicate that that would be OK, there is no certainty that it actually is"?
 
Furthermore, I don't really care what definitions can be found in dictionaries or any thesaurus.
Ah - the Humpty Dumpty approach. Jolly good.


When I add the word "seem" or "seemingly" into a sentence (let alone three times into the same sentence), I do so deliberately in order to indicate a lack of certainty. Virtually everyone will understand that such is my meaning/intention, and most of them will use the words in the same way for the same purpose themselves. If a dictionary or thesaurus indicates otherwise, I would say that it is the dictionary/thesaurus which is 'wrong' in terms of how our language is used.
I shall remember that last part, the next time you tell me that no matter what I think about the correct definition of a word (e.g. electrocution), dictionaries reflect reality, they do not prescribe.

But given your first statement, shall we take it that you don't care that the Collins English Dictionary 21st Century Edition describes seeming/seemingly as

apparent but not actual or genuine, outward or false appearance

?
 
So when you wrote this:
Seems alright, assuming all done correctly.
You didn't actually mean it only has the appearance of being all right but you are uncertain?

You were using "seems" in the way the thesaurus entry I posted earlier uses it?

As far as regulations are concerned, I don't think one has to look any further than 522.8.10. That seems to indicate very clearly that any cable with an earthed metal sheath may be directly buried,
Agreed.
Good job I got involved - you and John have been discussing this but you mean different things by 'seem/seemingly/etc'

John is adamant that he uses it to indicate that he is uncertain:
When I add the word "seem" or "seemingly" into a sentence (let alone three times into the same sentence), I do so deliberately in order to indicate a lack of certainty.

He meant that there is uncertainty over whether 522.8.10 indicates very clearly that any cable with an earthed metal sheath may be directly buried.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Status
Not open for further replies.
Sponsored Links
Back
Top