Thanks. However, that doesn't really answer my questions, because you have answered in terms of the requirements of BS7671, whereas my question was about the requirements of Part P of the Building Regs. As we all know, Part B does not specifically require compliance with BS7671. It only requires that those "reasonable provisions" be made for safety - and, whilst compliance with BS7671 might be taken as one way of demonstrating that such "reasonable provisions" had been made, nothing in the legislation says that this is the only way to comply.610.4 ... 631.1 ... 631.3 ... 633.1 ... So, John, in answer to your questions:
Yes, you would be required to undertake testing in your scenario ....
Nevetheless, you have effectively confirmed what I was saying - that many/most electricians would regard reasonably extensive testing as being necessary (for compliance with Part P) even following minor non-notifiable work. As you go on to say, that effectively means that, with a very small number of exceptions (like, I have to say, myself!), the great majority of non-notifiable DIY work is probably unlawful.
That raises another interesting question - to what extent should one have to seek pre-existing faults when making additions/changes to a circuit? If I take my car to a garage to have its brake pads replaced (clearly part of a safety-critical system), I doubt (and would not expect) that they would undertake inspection and testing of the remainder cof the braking system - and therefore that they could/would hand it back to me complete with any pre-existing faults in the hydraulic system (unless they noticed them by accident). With the added socket, provided that CPC continuity and polarity were correct (and ring continuity satisfactory if a ring has been 'interfered with'), it is all but certain that the resulting circuit will be no less satisfactory/safe than it was before the work was done, even if there were persisting (pre-existing) problems in relation to EFLI, RCDs, earthing/bonding etc., or even IR....- as a very minimum:
CPC continuity and polarity
Insulation Resistance
Earth Fault Loop Impedance
RCD operation (if the altered circuit is covered by an RCD)
Continuity and adequacy of installation earthing and bonding.
Kind Regards, John.