Thank you guys 
You have all gone to a lot of trouble to help me understand the reasons why an RCD is desirable in this situation and I really appreciate it – that’s what I wanted, a better understanding.
Fitting another enclosure would be tricky due to space constraints where the CU is located. It’s alongside a combi boiler so there is no space to the left. The right hand side is very close to the wall and the top is close to the ceiling. There is plenty of space underneath but cable lengths may come into play. Reorganisation within the CU is probably the only realistic option. I will take some further photos this afternoon and see whay you guys think.
I'm disappointed that the electrician did not come up with a better solution when they had the extension built. Although the CU was not moved, the cutout was so it would have been a simple matter for him to install another smaller CU at the time with plenty of room for expansion or even replace the existing one.
You have all gone to a lot of trouble to help me understand the reasons why an RCD is desirable in this situation and I really appreciate it – that’s what I wanted, a better understanding.
Fitting another enclosure would be tricky due to space constraints where the CU is located. It’s alongside a combi boiler so there is no space to the left. The right hand side is very close to the wall and the top is close to the ceiling. There is plenty of space underneath but cable lengths may come into play. Reorganisation within the CU is probably the only realistic option. I will take some further photos this afternoon and see whay you guys think.
I'm disappointed that the electrician did not come up with a better solution when they had the extension built. Although the CU was not moved, the cutout was so it would have been a simple matter for him to install another smaller CU at the time with plenty of room for expansion or even replace the existing one.