Hi
I plan to replace an 8kw shower with a 9.5kw one.
The house is around 13 years old.
Should I be concerned that the existing wires might not be able to take the extra power ?
many thanks
what size are the existin cables?
what size MCB/fuse is on the circuit?
You will probably need to replace the cable.
The likliest size to have been put in for an 8kW shower is 6mm², which is very borderline for 9.5kW.
Put in 10mm², and a 10.5kW shower....