I need to replace my shower it is 8.5kw and want to upgrade to 9.5kw. There is 10mm cable running to it with a 32A trip in the CU. Can the 32A trip be replaced with a 45A trip
Probably.I need to replace my shower it is 8.5kw and want to upgrade to 9.5kw. There is 10mm cable running to it with a 32A trip in the CU. Can the 32A trip be replaced with a 45A trip
Probably.I need to replace my shower it is 8.5kw and want to upgrade to 9.5kw. There is 10mm cable running to it with a 32A trip in the CU. Can the 32A trip be replaced with a 45A trip![]()
Is the circuit RCD protected?
Depends on the length of the cable and how it's installed - i.e. whether it is clipped to the surface of walls, buried in insulation, bunched with other cables etc etc.
This is a little out of date now, but it gives you the general idea....
http://www.tlc-direct.co.uk/Book/4.3.1.htm[/QUOTE]
Its within insulation, the cable length is approx 4m from the CU to the shower unit
The cable is 10mm wide.How do you know it's 100mm2 cable?