There is some misleading information in the link leading to unnecessary work.
Yes.Is it possible to power a single built-in 2.1kW zanussi oven off
an existing dedicated radial circuit (currently powering a combination microwave/oven rated at 3.4kW)?
5500/230 = 23.91 Amps but with cooking appliances we apply 'diversity' because all loads will not be on at the same time.Both appliances have a max power rating of 5.5 kW (or 3.4kW and
2.1kW).
All good - with the proviso of the cooker switch socket.Existing radial circuit has 16A mcb in consumer unit RCD protected, cable size is 6mm2 >> 45amp cooker isolation switch >> 45a dual appliance outlet >> 1). 3.4kW combi microwave hardwired, 2). 13A socket unswitched?
That's fine.Both appliances would be located within 2 metres of 45a cooker switch above.
Yes.Is it advisable to plug the 2.1kW oven into the unused 13A socket on existing 16A radial
Not unless cooker switch has an integral socket.or does the current setup need changing, i.e. mcb, etc, etc? Thanks
5500/230 = 23.91 Amps but with cooking appliances we apply 'diversity' because all loads will not be on at the same time.Both appliances have a max power rating of 5.5 kW (or 3.4kW and
2.1kW).
All good - with the proviso of the cooker switch socket.Existing radial circuit has 16A mcb in consumer unit RCD protected, cable size is 6mm2 >> 45amp cooker isolation switch >> 45a dual appliance outlet >> 1). 3.4kW combi microwave hardwired, 2). 13A socket unswitched?
That's fine.Both appliances would be located within 2 metres of 45a cooker switch above.
Yes.Is it advisable to plug the 2.1kW oven into the unused 13A socket on existing 16A radial
Not unless cooker switch has an integral socket.[/quote]or does the current setup need changing, i.e. mcb, etc, etc? Thanks
You could do that if you want. It won't hurt.Would it be advisable to have existing mcb in the consumer unit increased from 16A to 20A in order to be on a safer side load-wise and for future proofing purpose? Btw, I'm fully aware that this would be a notifiable work requiring a qualified electrician to do the job (Part P) if necessary.