where did you manage to get 34A from?
45A - 10A = 35A
35A x 0.3 = 10.5A...
so 10A + %30 of remainder ( 10.5A ) = 20.5A in my books?...
+another 5A if your switch has a socket..
I too was confused by the figures and agree with 20.5A. However I was taught to use 10A + 30% of max = 23.5A to give a little better margin.