Done by an East German electrician?The red looks to be the earth for some daft reason.
maybe it was an open circuit neutral and they used the sheath but that sounds a bit more dodgy!
It doesn't look like there is.I am assuming there is a conductor from the bottom of the henley sat on top of the cutout, coming from the cutouts L/H cable point,
It doesn't look like there is.I am assuming there is a conductor from the bottom of the henley sat on top of the cutout, coming from the cutouts L/H cable point,
View attachment 102484
And if the energy meter is showing that power is being used then the full load current from the Neutral meter tail will have to be passing along the red conductor, through the sensor and down into the lead sheath.
That's what I'm beginning to think is the case. Gonna see if I can pop round later and confirm. Got some shields for that Wylex to put on too