Sparking on earth cable

Joined
20 Oct 2020
Messages
46
Reaction score
2
Country
United Kingdom
Hi

I have changed one of my mcbs and were connecting earth back to main terminal and saw a small spark. What could it be ?

Thanks
 

Attachments

  • 20261107_101849.jpg
    20261107_101849.jpg
    358.4 KB · Views: 46
  • Screenshot_20261107_104543_Gallery.jpg
    Screenshot_20261107_104543_Gallery.jpg
    85 KB · Views: 46
  • 20261106_221846.jpg
    20261106_221846.jpg
    415.5 KB · Views: 46
Which earth connection is it?

The main one to the earth spike/mains water?
Or to an in-house circuit?
 
DNO earth and real earth are not the same, the home should be bonded to DNO earth, but if items have been incorrectly bonded, then there can be a voltage difference between two earth types, also if not RCD protected there can be an earth fault. But also capacitive linking can cause a small spark when connecting, but this should not show a second time.

So you have highlighted a potential fault, so now you need to used the test equipment to find out why, so get out the loop impedance tester, and insulation tester, and see what has caused it. May want to clamp on an ammeter to see how much current is flowing, and it the current still flows with the isolator switched off.
Diffrence line neutral 8 Feb 24 reduced.jpg
I do check back ground leakage, once you know how much current is flowing and the voltage difference you will have some idea as to what is causing it.

However, since you have asked the question, it seems likely you need to employ a proper electrician to investigate further.
 
This is connected to pme
 

Attachments

  • Screenshot_20261107_114514_Gallery.jpg
    Screenshot_20261107_114514_Gallery.jpg
    444.4 KB · Views: 23
I have changed one of my mcbs

Why?

I’m going to guess that maybe it was tripping, and so you decided it was faulty and should be replaced.

and were connecting earth back to main terminal

Why did you disconnect it in the first place?

and saw a small spark. What could it be ?

A warning of imminent death. Frankly I’m amazed that you got your phone out to capture the image of the spark with your thumb on the wire, rather than retreating to a safe distance.

Was the isolator that is shown in your later picture turned off?

One thing that’s not clear in any of your photos is whether there is bonding to the water & gas supplies. Is there a main earth terminal? Are they connected inside the CU?
 
One thing that’s not clear in any of your photos is whether there is bonding to the water & gas supplies. Is there a main earth terminal? Are they connected inside the CU?

Good spot, also the earth by the isolator and the earth in the consumer unit look like different cables....must/might be an earth terminal somewhere.
 
pete01 mcb was on and the earth cable from this ring sparked when connected to terminal in cu
 
You should get an electrician to sort that out for you, I take it that you are not a registered electrician and you should not be inside the consumer unit. You have an earth fault on your system, possibly isolated to one circuit but quite possibly on them all. Have you been doing any other alterations or changing light fittings or light switches by any chance?
 
No i havent but live to earth test when disconected from earth block showed me 130v
 