This is a sub-main. The enclosure you see has a 63A RCD inside. There is no means of fusing down.The RCD is fed from the Henley and the cable you see at the bottom is SWA.
![]()
The cutout has no seals, nor the meter for that matter. The seals are missing because the black cable is a very poor DIY attempt at PME'ing a TT supply. The cable has been attached directly to the neutral block rather than the earth block present at the top of the cut-out.
As an aside, there are no meb's to the property, either. Lord knows what would happen if the supply neutral were to drop out.....And as for that DIY PME, if the supply is not suitable for conversion (ie the supply neutral is not grounded in several places), what then?![]()
![]()
The supply to the top of the cut-out is the TT supply from outside. The lower pair go to the Henley. Then a pair go to the meter, which feeds an old Wylex board & one submain. The third pair of tails off the Henley (ie UNMETERED) feed that unfused submain in the first picture.
Nice, eh?