Yes, I understand that. What I was 'struggling' with is the high degree of 'voltage de-rating' for DC. Once ionisation has occurred, is the arcing not primarily current-, rather than voltage-dependent - or have I got that wrong?
Yes, I understand that. What I was 'struggling' with is the high degree of 'voltage de-rating' for DC. Once ionisation has occurred, is the arcing not primarily current-, rather than voltage-dependent - or have I got that wrong?
That is correct for part of the process. Ionisation essentially presents a low resistance path since there are plenty of liberated electrons and ions which act as charge carriers.
Now I don't have any numbers easily available at the moment so I'm going to make them up (at the risk of being attacked for doing so
That very same principle is used to start florescent lamps.
Now, if you have a closed switch contact (let's say carrying 100 volts DC with a load current of 50 amps. When the switch is opened the following process tends to follow
1) The amount of contact area is reduced slowly (slow in relative terms)
2) The reduced contact area will increase contact resistance and therefore volt drop across the contacts.
3) As the contact area is almost open the residual contacting material will start to get very hot (and ultimately flash off- look up wetting current) This part is a function of the load current.
4) As that residual hot metal finally disconnects, an arc is struck utilising a combination of electrons from the thermionic emission process and electrons from the heated gas at the contact site.
5) Now the ionisation has a higher resistance than that of the metal-metal contacts so the circuit resistance is going to increase making the low load resistance less of a factor. At this point the potential difference and the final contact gap will be the major factors for how long the arc will persist.
Well the contact material will factor significantly too.
It has been a very long time since I looked at such events so I am sure I have missed something but in general that is roughly the process.
There is also a problem of stored energy in inductive parts of the circuits but that's for another day.
Finally if the voltage applied were AC then the arc would almost certainly extinguish at the first zero crossing.
So it is the voltage which is used quite often to derate an AC switch for DC applications. However, in my personal experience AC switches do a good job in many DC applications.