Storage Heater Insulation Resistance

Discussion in 'Electrics UK' started by studentspark, 7 Apr 2018.

  1. studentspark

    studentspark

    Joined:
    13 Mar 2010
    Messages:
    589
    Thanks Received:
    15
    Location:
    London
    Country:
    United Kingdom
    Four new storage heaters

    Instructions say The Dielectric IR at 500v must be at least 0.5Mohms

    Im getting 2Mohms , L- E, and N-E on three of them, and 0.6Mohms on the other.

    This is testing the heaters alone, not wired to the supply.

    Are these IR results to be expected. They seem very low, especially L-E

    Thanks
     
  2. Sponsored Links
  3. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    73,459
    Thanks Received:
    4,230
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    Which resistance is higher?

    0.5MΩ or 2.0 MΩ?
     
    • Like Like x 2
  4. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,341
    Thanks Received:
    878
    Country:
    United Kingdom
    According to the instructions, yes. But you could call the technical line to clarify. They seem low to me too, but maybe there's a technical reason for it, hence why they documentsd such a relatively low value
    2.0M of course, why do you ask?
     
    • Thanks Thanks x 1
  5. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,490
    Thanks Received:
    402
    Location:
    Devon
    Country:
    United Kingdom
    Elements kept in storage for some time will absorb moisture, also from manufacture. After a few days of use the moisture will be driven out and the readings will improve.
     
    • Thanks Thanks x 1
  6. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    5,259
    Thanks Received:
    307
    Country:
    United Kingdom
    Are you testing from the incoming terminal block, are all your input controls set to max, the element casings are not in contact with earth apart from possible contact with the bricks, and then through the insulation
     
    • Thanks Thanks x 1
  7. studentspark

    studentspark

    Joined:
    13 Mar 2010
    Messages:
    589
    Thanks Received:
    15
    Location:
    London
    Country:
    United Kingdom
    I was wondering if there was some electronic component, a suppressor or such to reduce noise?
    Have no idea on electronics , so could be talking nonsense.

    Yes testing at the incoming terminals.
    Thanks for the suggestion
     
  8. Sponsored Links
  9. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    5,259
    Thanks Received:
    307
    Country:
    United Kingdom
    Some heaters have an accelerator heater on the bi metal strip / flap control, I assume these are standard heaters and not the new all singing type
     
  10. studentspark

    studentspark

    Joined:
    13 Mar 2010
    Messages:
    589
    Thanks Received:
    15
    Location:
    London
    Country:
    United Kingdom
    Yes, Standard heaters , not the new electronic thermostat controls. Manufactured by Olsberg
     
  11. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
     
  12. studentspark

    studentspark

    Joined:
    13 Mar 2010
    Messages:
    589
    Thanks Received:
    15
    Location:
    London
    Country:
    United Kingdom
    Putting large metal boxes in every room, you would want them to be properly earthed, and a value of 0.5mohms on an appliance would concern me.
    The manufactures state this as a minimum. I was more interested in the reasons for the low IR values.
     
  13. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    They will be if installed properly.


    What's the worst case fault current?


    As per Lectrician - run them for a few days and test again.
     
  14. studentspark

    studentspark

    Joined:
    13 Mar 2010
    Messages:
    589
    Thanks Received:
    15
    Location:
    London
    Country:
    United Kingdom
    Yes I plan to, thanks
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page