So by that logic, had the main wiring been 2.5 mm2 (and for arguments sake the flex in 1.5 mm2) we would still be satisfied that the RCBO was 32 amp?
I think so (even possibly with 1.5mm² fixed wiring, if Zs was low enough - see below) - provided that one is happy that the load is "not likely to resulting an overload" and provided that Zs is low enough to satisfy fault protection requirements - since one can then invoke one of the bits of 433.3.1. (sorry, away from regs - so can't tell you which bit!)So by that logic, had the main wiring been 2.5 mm2 (and for arguments sake the flex in 1.5 mm2) we would still be satisfied that the RCBO was 32 amp?
The largest heater is 3.4kw what are the others ? And should they be fitted with FCU's ?
DS
As we've discussed before, if you are concerned that the load may create an overload, that makes sense - but (unless MIs complicate the issue) the regs do not require it, being perfectly happy so long as the cables are adequately protected (and, as I've just written, not even requiring overload protection of the cables if one judges that overload is "unlikley").The largest heater is 3.4kw what are the others ? And should they be fitted with FCU's ?
Do not cover.I would check what the manufacturer's instructions require.
Leave it alone. The mans done a lovely job
Although the bus bar covers missing
Yes it is! Refit it with the main switch off.
Are you reading the top of the heater !Do not cover.I would check what the manufacturer's instructions require.