Had a job today, customer reported sparks from an earth wire to the water pipe. When I got there, the main bond to the water had been cut off as there were building works and plumbing going on, and the earth was arcing across a bit to the copper pipe in the ground.
Its a PME supply, but even with the main switch off at the DB still got the arcing. I insulation tested the circuits and had one ring down to 0.03M neutraul to earth. After getting everything unplugged and switched off the fault had cleared , but on plugging things back in, the fault didnt return.. however in the mean time I had my apprentice re do the main bond to the small bit of copper in the ground and run a new 10mm to the new stopcock position (conneted to the old pipe in plastic.)
Have I missed something here a bit obvious, or is it OK. The fact I still had arcing with the main switch off is a bit odd?? It stopped when I temporarily disconnected the main earth from the cut out..
Its a PME supply, but even with the main switch off at the DB still got the arcing. I insulation tested the circuits and had one ring down to 0.03M neutraul to earth. After getting everything unplugged and switched off the fault had cleared , but on plugging things back in, the fault didnt return.. however in the mean time I had my apprentice re do the main bond to the small bit of copper in the ground and run a new 10mm to the new stopcock position (conneted to the old pipe in plastic.)
Have I missed something here a bit obvious, or is it OK. The fact I still had arcing with the main switch off is a bit odd?? It stopped when I temporarily disconnected the main earth from the cut out..