- Joined
- 11 Jan 2004
- Messages
- 47,115
- Reaction score
- 4,107
- Country
Went to an RCD fault yesterday.
The RCD was tripping intermittently.
On testing the RCD from a socket outlet, it refused to trip on the 1 x test.
The Zs was ok (0.9), Ze 60.9 (subterranean TT).
When testing the unit in isolation, it performed perfectly.
Disconnected each circuit in turn. On disconnecting the lighting, the RCD again tested perfectly.
Found a dead N/E short on the lighting which, when rectified & lighting reconnected, sorted the problem.
Now here's an extra twist.
One socket in the lounge is used for the vacuum. Every time it was switched on using this socket, the RCD used to trip (before we rectified the lighting fault). In any other socket, it would work OK. The socket had a good Zs (0.92), polarity OK & connections good & tight.
What's that all about