Supply lighting circuit via fused spur on ring

Discussion in 'Electrics UK' started by julioarca, 25 Nov 2009.

  1. julioarca

    julioarca

    Joined:
    4 Nov 2007
    Messages:
    97
    Thanks Received:
    0
    Country:
    United Kingdom
    Is it permissable to feed a lighting circuit from a ring mains via a fused spur?

    If so what must be put in place to allow this etc.
     
  2. Sponsored Links
  3. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    37,154
    Thanks Received:
    1,290
    Country:
    United Kingdom
    Yes.

    A fused spur!

    If possible, wire the fused spur into the ring final circuit. Then on the load side of the spur, use a fuse suited to the total load and choose the cable accordingly.

    If you want, you can use a switched spur to switch the lighting direct from that switch or you could use a an unswitched fused spur to feed the lighting via a plateswitch.
     
  4. mikeyd

    mikeyd

    Joined:
    17 Jul 2007
    Messages:
    792
    Thanks Received:
    76
    Country:
    United Kingdom
    Yes.

    A fuse in the fused spur which is suitable for the lighting circuit.

    Edit: I Must learn to type with more than one finger..
     
  5. julioarca

    julioarca

    Joined:
    4 Nov 2007
    Messages:
    97
    Thanks Received:
    0
    Country:
    United Kingdom
    what labels would need to be in place?
     
  6. EdwardCurrent

    EdwardCurrent

    Joined:
    29 Apr 2007
    Messages:
    907
    Thanks Received:
    22
    Country:
    United Kingdom
  7. mikeyd

    mikeyd

    Joined:
    17 Jul 2007
    Messages:
    792
    Thanks Received:
    76
    Country:
    United Kingdom
    Sorry, not sure I understood the original question. Why do you think it needs a label?
     
  8. Sponsored Links
  9. julioarca

    julioarca

    Joined:
    4 Nov 2007
    Messages:
    97
    Thanks Received:
    0
    Country:
    United Kingdom
    I am sorry for my impoliteness, thnx guys for the help, it is much appreciated
     
  10. EdwardCurrent

    EdwardCurrent

    Joined:
    29 Apr 2007
    Messages:
    907
    Thanks Received:
    22
    Country:
    United Kingdom
    ;)

    Can I just ask if the circuit that you are 'picking' these lights up from is RCD protected ?

    Regards
    Ed
     
  11. julioarca

    julioarca

    Joined:
    4 Nov 2007
    Messages:
    97
    Thanks Received:
    0
    Country:
    United Kingdom
    it is rcd, 30mA protected, thnx

    Can I just ask if the circuit that you are 'picking' these lights up from is RCD protected ?

    Regards
    Ed[/quote]
     
  12. Spark123

    Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,841
    Thanks Received:
    474
    Location:
    Cumbria
    Country:
    United Kingdom
    It is imo a poor setup to have lighting circuits spured from a ring circuit. It is OK for say a couple of fluorescents for say under unit lighting but I'd edge away for using it for a full circuit.
    It is better to have them from the consumer unit so the installation is divided into circuits to avoid inconvenience.
     
  13. julioarca

    julioarca

    Joined:
    4 Nov 2007
    Messages:
    97
    Thanks Received:
    0
    Country:
    United Kingdom
    I would agree but the floor is blockboards and its only to feed 2 lights in a new extension
     
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page