I need a to get some estimates for the wiring of a new garage, but I want to check what might me needed before I do.
The house is wiring is TT single phase and was been installed about 15 years ago.
The garage is 35m away from the CU.
I was thinking of a small radial and lights.
What I think needs to be quoted for is
Installing of 4mm or 6mm SWA earthed only at the house
A new ground spike installing at the garage
A 40A isolator without rcd on the incoming supply to protect the cable
A cu in the garage with a 32A mcb going to
6A mcb - lighting
16A rcbo - sockets
The cabling in the garage to be done radial with conduit or trunking and metal clad sockets.
The garage also has a metal outside tap supplied by a plastic pipe, this may need earth bonding to?
The supply can be isolated at the meter.
If the trench is already dug will this job need about 2 days labour?
Is there anything else required?
The house is wiring is TT single phase and was been installed about 15 years ago.
The garage is 35m away from the CU.
I was thinking of a small radial and lights.
What I think needs to be quoted for is
Installing of 4mm or 6mm SWA earthed only at the house
A new ground spike installing at the garage
A 40A isolator without rcd on the incoming supply to protect the cable
A cu in the garage with a 32A mcb going to
6A mcb - lighting
16A rcbo - sockets
The cabling in the garage to be done radial with conduit or trunking and metal clad sockets.
The garage also has a metal outside tap supplied by a plastic pipe, this may need earth bonding to?
The supply can be isolated at the meter.
If the trench is already dug will this job need about 2 days labour?
Is there anything else required?