System balancing when TRV's are fitted

Joined
15 Apr 2012
Messages
507
Reaction score
35
Location
London
Country
United Kingdom
I have just replaced 8 rads and fitted TRV's. I balanced the system by just feeling the warmth at each rad and now they all heat up at the same rate.

Do I need to do anymore? do I need to check actual temp drops at each rad? It seems to me that TRV's will always affect the balancing due to them continually opening and closing, so an accurately balanced system is pointless.

Am I right or wrong?
 
Sponsored Links
You should balance with all the TRVs fully open.

Con boiler to 15 C diff temp and non-con boiler to 11 C.

You can guess the diff with hands if you don't have a contact digi thermometer.

Tony
 
It seems to me that TRV's will always affect the balancing due to them continually opening and closing, so an accurately balanced system is pointless.

Am I right or wrong?
TRVs are not like a switch, on or off. They are more like the volume control on your TV: if it's too loud you turn it down a bit and vice versa. But in the case of the TRV it's fully automatic, keeping the room temperature constant by adjusting the flow through the radiator. If the system is correctly balanced, a change in the flow through one rad will have little effect on the other rads.

According to Drayton

Failure to correctly balance a system can lead to complaints of inefficient operation and criticism of the operational abilities of thermostatic radiator valves, when in fact the valves are not the source of the problem. Common complaints raised by home owners include:

• Rooms are slow to reach temperature even though radiators are sized correctly
• Some rooms with correctly sized radiators never reach temperature during cold periods
• Room temperatures fluctuate particularly if the TRV is on a low setting

It must be remembered that no amount of commissioning and adjustment will compensate for a poorly designed or installed system. There is no substitute for good design.
 
TRVs are not like a switch, on or off. They are more like the volume control on your TV: if it's too loud you turn it down a bit and vice versa. But in the case of the TRV it's fully automatic,]

No they are not.

They turn the rad on or off, but should maintain the ROOM at a desired temperature.
 
Sponsored Links
I have to agree somewhat with Fireman, when a TRV reaches the desired temperature that it has been set to, it turns the flow to the radiator off, when it cools below the setting it opens again to restore the flow.

http://www.radiatorcontrol.com/gas_filled_design_works.aspx

That being said I suppose they are variable depending on how far the spindle is pushed by thermostatic valve...hmmmm...scratch that, they would be graduated.
 
No they are not.
They turn the rad on or off, but should maintain the ROOM at a desired temperature.

Oh, yes they are!

They're a modulating control device that can vary from 0 to 100% open. In either extreme they will be fully open or fully closed, but they usually modulate to regulate the flow to maintain the required temperature.

http://heating.danfoss.co.uk/xxNewsx/759716fc-82db-4be4-bc4a-0e18ab022edb.html

"The TRV’s control action is modulating, i.e. it makes appropriate slight adjustments to the valve spindle position to increase or reduce the volume of heated water passing through the individual radiators."

You can get thermostatic controls that go from fully open to fully closed in one movement (car thermostat valves, T&PRVs) but TRVs usually move gradually in response to temperature changes.
 
The ideal is that they will more proportionally to give the exact flow which will maintain the set room temp.

In practice that will not always occur when humans are there as well. Opening dfoors/windows etc.

They can often overshoot and turn on/off but that's not really relevant to the occupiers as its the final room temperature that is important.

Tony
 
TRVs are not like a switch, on or off. They are more like the volume control on your TV: if it's too loud you turn it down a bit and vice versa. But in the case of the TRV it's fully automatic,]
No they are not.

They turn the rad on or off, but should maintain the ROOM at a desired temperature.
I'm not going to repeat what others have said but a fuller explanation can be found in Balancing of Radiator Systems, particularly section 2.4.
 
Links in this post may contain affiliate links for which DIYnot may be compensated.

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top