Extending an existing ring main which is on 2.5mm2 T&E, my only reasonably easy route for the extra cable is within an insulated 250mm thick (!) stud wall.

Referring to table 4D5A, I see that the existing 2.5mm2 T&E is rated at 27A if clipped direct. The same table lists 4mm2 routed in an insulated wall at the same figure - 27A.

All other things being equal, am I OK to use 4mm2 T&E for this part of the circuit, or am I missing something vital?

Cheers.
 
Sponsored Links
no problem to use larger cable for parts of a cuircuit to account for thermal insulation.
 
I suppose what I really meant to ask was whether 4mm2 is large enough for a cable totally enclosed in a thermally-insulated wall?
 
2.5mm² is rated 21A (for method 15) which still complies with regulation 433-02-04.
 
Sponsored Links
Thanks for that Spark. I've just found that out from another source as well. Typically I have now bought a reel of 4mm2 and started the job this afternoon. Never mind...

The only potential problem now is handling the connections - two, or even three 4mm2 conductors in one terminal will be tight, but I hope manageable.

Thanks again.
 
rustus said:
The only potential problem now is handling the connections - two, or even three 4mm2 conductors in one terminal will be tight, but I hope manageable.

Thanks again.

BS1363 requires the outlets to hold 3x2.5mm² conductors, or 2x4mm² conductors, so two shouldn't be a problem, and not quite sure why you want 3?
 
Spurs, probably. But best to put every outlet on the ring, then no need for spurs....
 
securespark said:
Spurs, probably. But best to put every outlet on the ring, then no need for spurs....

Yeah, my line of though was that if he is 're-jigging' the ring, why is it going to end up with spurs on it...
 
Spurs, as guessed, but I only envisage one - to an external Masterseal socket with single rear cable entry (optional back plate).
 
MK claim their sockets can take 3x4mm though i'd imagine a deep backbox would be in order.
 