But do you get RCD's with such a high trip current. In 7671, 300mA seems the highest.
Im sure in the industrial / specialist world all manor and scale of things happen.
This one you can wind up to 10amp
Im no expert but i think the point is too protect the tails etc on TT systems from the main switch to the dist boards etc more so where the cables are in metal trunking
I think the regs say the rcd can be omitted if the cables, prior to a board fitted with 30ma rcds, are reinforced or Double insulated
531.3.5.2.201