Testing a Log Cabin installation

Joined
22 Sep 2007
Messages
16
Reaction score
0
Location
Bristol
Country
United Kingdom
Perhaps someone can help. Probably being thick, but anyway.....
4mm SWA from MK split load CU, connected via 32A MCB on non RCD side.
SWA teminates in a mini MK CU fitted with a 63A main CB with RCD protection, in the log cabin.
32A MCB for ring.
6A MCB for lights.
Obviously, from the CU in the log cabin, I carry out tests as per house.
My question is, how do I test the SWA and how would I write the results down on the EIC?
I'm testing with a Megger 1552.
Thanks
 
Sponsored Links
Wouldn't you treat the outgoing SWA as a circuit on the house CU, describe its function on the schedule as "Log Cabin" or similar, and record all the details (over-current device, size, test results etc) for the SWA cable, and then have a separate schedule sheet for the circuits within the cabin?
 
Thanks Ban.
Thought I was being thick!
It's strange sometimes how you just can't see the wood for the trees !!
Cheers
 