I got it at last today - the big red book and I will be studying it rigorously over the next few days.Watch this space folks.....................................
Is that still the case if cables are buried at a depth less than 50mm and not protected by an earthed metallic conduit or similar>
Not quite......
Not as simple as saying "these sockets are for that".
.
I see supplementary bonding is still allowed if not protected by RCD on existing installations.
That is, supplementary bonding is required, unless the three provisions of 701.41.2 are met.
And it is not an either/or situation because 701.411.3.3 requires RCD protection for all circuits in the location whatever the state of bonding.
Just thinking of a situation where someone asks for new lights & an ext fan in the bathroom & you got to RCD it![]()
I see supplementary bonding is still allowed if not protected by RCD on existing installations.