I'm not sure where all this has come from.. the OP is having problems with an old voltage operated circuit breaker, .
I am not sure where you got that impression. At no point has the OP said he is having any problems with anything at all. All he asked is should he RCD it. To which the answer is yes.
Really?
It is my understanding that where a earth rod is used all circuits must run off a RCD. However we get regular power cuts and I want the freezer on when the power comes back. 17th edition combined with a TT system appears to mandate the use of RCDs on all circuits. Which would prove to be a pain.
If I replace the CU I will need to purchase an active 100mA RCD so that it won't trip when the power fails? The sockets would need to be active as well? On one hand I want to update it on the other hand leave well alone.
My understanding was that the OP is having problems with the VOCB failing to automatically restore the supply after a power cut. He/she does not want an RCD specifically for the protection that it offers. Replacing it with a passive 100mA RCD should not only overcome that problem, but also offer a greater degree of protection than that already present.
Would you use an electric shower knowing there is an EFLI of 60 ohms or more with no 30mA RCD in place? I wouldn't.
I doubt that any equipotential bonding has been carried out. that would mean that fault current could light up the copper pipework.
Do you think an electric shower with 100mA RCD upfront is going to be, by any significant degree, any more or less safe than a TN-C-S install to the 16th edition with no RCD protection on the shower circuit at all?
I stand by what I said before, it is advisable to 30mA RCD the shower circuit, but the OP is under no impetus to do so.