Does anyone have any views /experience on/of the above re unstable HW outlet temperatures even with a perfectly operating thermostat which is the same length as the heating element.
My views.
With this top mounted immersion you will only heat the full immersion length of the cylinder from a fully cold cylinder.
20/25% of the HW must then be drawn off before the stat will cut back in, for example, with a stat setpoint of 60C and assuming 50C cut in, (hysteresis of 10C), and a cold mains of 15C then ~ 22% of the HW must be drawn off to enable the stat to cut in. If 22% of the HW is drawn off, enough to get the the stat to start calling at 50C then the top 78% will/can still be at 60C with the remaining 22% at 15C then the actual final HW temp will/can be higher than 60C because the vertical element will heat the cylinder without any destratification and you may end up with 78% at 70C and the remaining 22% at 25C on stat cut out. Finally if say 60% HW is then drawn off leaving 40% at 70C (and 60% at 15C) then if the cylinder is reheated its possible to have 40% at 87C and 60% at 42C, very close to the hi limit stat trip but the control stat should still have cut out at a average of 60C?. (0.4*87)+(0.6*42).
I have a 53 year old dual element top mounted immersion but only use the shorter element which heats 30L, it doesn't have the rod type stat but has a surface mounted one on top of the immersion so I can't carry out any tests, almost the full 30L has to be used before the stat cuts back in but it does give a very stable HW temperature of 65C.
My views.
With this top mounted immersion you will only heat the full immersion length of the cylinder from a fully cold cylinder.
20/25% of the HW must then be drawn off before the stat will cut back in, for example, with a stat setpoint of 60C and assuming 50C cut in, (hysteresis of 10C), and a cold mains of 15C then ~ 22% of the HW must be drawn off to enable the stat to cut in. If 22% of the HW is drawn off, enough to get the the stat to start calling at 50C then the top 78% will/can still be at 60C with the remaining 22% at 15C then the actual final HW temp will/can be higher than 60C because the vertical element will heat the cylinder without any destratification and you may end up with 78% at 70C and the remaining 22% at 25C on stat cut out. Finally if say 60% HW is then drawn off leaving 40% at 70C (and 60% at 15C) then if the cylinder is reheated its possible to have 40% at 87C and 60% at 42C, very close to the hi limit stat trip but the control stat should still have cut out at a average of 60C?. (0.4*87)+(0.6*42).
I have a 53 year old dual element top mounted immersion but only use the shorter element which heats 30L, it doesn't have the rod type stat but has a surface mounted one on top of the immersion so I can't carry out any tests, almost the full 30L has to be used before the stat cuts back in but it does give a very stable HW temperature of 65C.