Trianco oil boiler problem

Joined
17 Nov 2026
Messages
2
Reaction score
0
Country
United Kingdom
Hi, my Trianco contractor 50/90 oil boiler sounds like it has to keep lighting itself. The Grundfos pump has one green and 2 amber lights on. It warms the radiators but it obviously has a problem. The boiler was serviced just before summer. Any ideas what can be causing it. I know that spare parts are very limited as it is now obsolete. Thanks.
 

Attachments

  • IMG_8624.jpeg
    IMG_8624.jpeg
    675.5 KB · Views: 3
First its very doubtful the grundfos pump if anything to do with burner cutting out.
First check photocell on burner is clean.
As burner is cutting out and restarting check for decent flow of kerosene.
We look after a number of these boilers parts readily available .
 
Cover off burner photocell is pushed into burner so it senses light.
Cable from it goes back to control box.
Lots of exploded diagrams on line and spares lists.
Instalation manual also useful that includes a fault finding chart.
 