Shower intermittently goes cold. 2 - 3 times during use, appears worse if the heat is increased. Have changed the shower head, and don't think it's low pressure as light is not on and have another Triton shower off the same water supply.
He's a mere boy...L.Spark said:1311 posts! blimey you should be promoted
46A should not melt 6mm²cable connected to it was 6mm, backed up by 30A cartridge fuse
Even so. Method 1 regards embedded in plaster as the same as clipped direct, and even with Method 6 6mm² should be good for 32A.L.Spark said:46A is Clipped Direct BAS...
This was tiled over and plastered in the wall, only place it was clipped was for a couple of meters in the cupboard under the stairs.
Good for them. Smart move too, as that means that they can sell you a bigger one next time round.....L.Spark said:Triton reccomend 10mm cable for 8.5kw showers and above!
ban-all-sheds said:Good for them. Smart move too, as that means that they can sell you a bigger one next time round.....L.Spark said:Triton reccomend 10mm cable for 8.5kw showers and above!