Hi all
My first post on here! Have read loads of useful info but couldn't find the answers to my problems so thought I'd put it to you all. Hope someone out there can help.
We have a fairly complicated sealed system installed in our house and I'm tearing my hair out trying to resolve issues that have been ongoing since it was installed 2 years ago. I now realise the original installer wasn't up to the job, but he's since moved abroad and left me to pick up the pieces.
In a nutshell, we have got through 2 heat exchangers in our boiler in as many years. Same problem both times; the heat exchanger leaks system water across into the condensate resulting in rapid loss of pressure and frequent topping up. Both myself and the boiler engineers are completely at a loss to understand how this could happen twice in a brand new boiler, and so I've been looking at the system design to see whether we have a design fault somewhere that could be contributing to it.
The system comprises a Worcester Greenstar 40CDI conventional coupled to a 280 Litre Thermostore cylinder which provides the DHW and also the underfloor heating in 2 zones of the house. The rest of the house (a further 3 zones) is heated by standard rads, a whopping 22 of them in total which are run directly off the flow/return of the boiler with zone valves on the flow. It was a completely new system/rads/pipework 2 years ago. The Thermostore was originally installed because we were going to fit solar hot water panels, but this never materialised so in effect the Thermostore wasn't really necessary/the best option, but we'd already bought it and it had been fitted.
The Thermostore requires the boiler to operate at maximum output (88 degrees) in order to provide good DHW recovery. Not ideal given that I thought condensing boilers worked most efficiently around the 60 degree mark? Anyway, if the boiler is turned down the DHW is depleted fairly quickly and recovery is slow but at maximum output the DHW is really good. Naturally, running the system at max output means that all the rads get unnecessarily hot (dangerously hot) and causes a fair amount of expansion in the system. It also means that when the boiler is running hot and then all the zone valves close (because the zones have reached temp) there is a lot of heat remaining in the boiler. To deal with this the main pump has an overrun for a few minutes, and there is an automatic bypass valve which feeds a dedicated bypass radiator circuit. However, this bypass circuit does not always seem to operate and occasionally the boiler has overheated and let off steam from its auto bottle vent.
There is an expansion vessel on the pipework, although I notice this is only an 18L vessel and I also notice it's connected to the flow pipe AFTER the auto bypass valve. I have read elsewhere on this forum that it should be potentially much bigger (perhaps 50L?) and also fitted on the return pipework? I have checked the expansion vessel works ie. no water from the valve.
I have a number of questions:
1. Any ideas why any of the above would cause the heat exchanger problem mentioned? Would running the system at max output be a bearing factor or should it be capable of this?
2. Is the 18L expansion vessel and it's position in the system adequate? If not what should I fit, and where in the system?
3. Why would the auto-bypass valve sometimes not operate?
4. Can anyone suggest a way in which I can alter this system fairly simply so that I can run the boiler at max output but have the rads run at a more reasonable temp?
5. We are going to have to drain, clean and refill the system in order to change the heat exchanger again. Do you have any guidance on how much inhibitor to use in a system of this size? I was going to use Sentinel X100 - is this a good choice? We have noticed that the existing system water is a murky brown colour, not good at all. We can only assume this is because of the frequent re-filling that has diluted the existing inhibitor which has effectively been lost down the condensate pipe.
6. We recently fitted a water softener. Can I (should I?) refill the system with softened water? I have seen confilcting advice on this point and wonder if anyone has first hand experience of it.
I apologise for the enormous post, but hope someone out there can shed some light on these problems.
Cheers
My first post on here! Have read loads of useful info but couldn't find the answers to my problems so thought I'd put it to you all. Hope someone out there can help.
We have a fairly complicated sealed system installed in our house and I'm tearing my hair out trying to resolve issues that have been ongoing since it was installed 2 years ago. I now realise the original installer wasn't up to the job, but he's since moved abroad and left me to pick up the pieces.
In a nutshell, we have got through 2 heat exchangers in our boiler in as many years. Same problem both times; the heat exchanger leaks system water across into the condensate resulting in rapid loss of pressure and frequent topping up. Both myself and the boiler engineers are completely at a loss to understand how this could happen twice in a brand new boiler, and so I've been looking at the system design to see whether we have a design fault somewhere that could be contributing to it.
The system comprises a Worcester Greenstar 40CDI conventional coupled to a 280 Litre Thermostore cylinder which provides the DHW and also the underfloor heating in 2 zones of the house. The rest of the house (a further 3 zones) is heated by standard rads, a whopping 22 of them in total which are run directly off the flow/return of the boiler with zone valves on the flow. It was a completely new system/rads/pipework 2 years ago. The Thermostore was originally installed because we were going to fit solar hot water panels, but this never materialised so in effect the Thermostore wasn't really necessary/the best option, but we'd already bought it and it had been fitted.
The Thermostore requires the boiler to operate at maximum output (88 degrees) in order to provide good DHW recovery. Not ideal given that I thought condensing boilers worked most efficiently around the 60 degree mark? Anyway, if the boiler is turned down the DHW is depleted fairly quickly and recovery is slow but at maximum output the DHW is really good. Naturally, running the system at max output means that all the rads get unnecessarily hot (dangerously hot) and causes a fair amount of expansion in the system. It also means that when the boiler is running hot and then all the zone valves close (because the zones have reached temp) there is a lot of heat remaining in the boiler. To deal with this the main pump has an overrun for a few minutes, and there is an automatic bypass valve which feeds a dedicated bypass radiator circuit. However, this bypass circuit does not always seem to operate and occasionally the boiler has overheated and let off steam from its auto bottle vent.
There is an expansion vessel on the pipework, although I notice this is only an 18L vessel and I also notice it's connected to the flow pipe AFTER the auto bypass valve. I have read elsewhere on this forum that it should be potentially much bigger (perhaps 50L?) and also fitted on the return pipework? I have checked the expansion vessel works ie. no water from the valve.
I have a number of questions:
1. Any ideas why any of the above would cause the heat exchanger problem mentioned? Would running the system at max output be a bearing factor or should it be capable of this?
2. Is the 18L expansion vessel and it's position in the system adequate? If not what should I fit, and where in the system?
3. Why would the auto-bypass valve sometimes not operate?
4. Can anyone suggest a way in which I can alter this system fairly simply so that I can run the boiler at max output but have the rads run at a more reasonable temp?
5. We are going to have to drain, clean and refill the system in order to change the heat exchanger again. Do you have any guidance on how much inhibitor to use in a system of this size? I was going to use Sentinel X100 - is this a good choice? We have noticed that the existing system water is a murky brown colour, not good at all. We can only assume this is because of the frequent re-filling that has diluted the existing inhibitor which has effectively been lost down the condensate pipe.
6. We recently fitted a water softener. Can I (should I?) refill the system with softened water? I have seen confilcting advice on this point and wonder if anyone has first hand experience of it.
I apologise for the enormous post, but hope someone out there can shed some light on these problems.
Cheers