I spent hours yesterday evening reading about this and I am amazed (and intrigued) at how complicated it is. I already respected plumbers but now, woah, this is serious stuff!
Anyway, could someone help me understand this:
I have a new gas combi boiler, 30kw
When it was installed the plumber did a benchmark and noted down CH outflow temperature of 70C and return flow of 67C
This return flow seems too high to me. I currently have the CH outflow set to 60C as the manufacturer (Worcester Bosch) suggests condensing will only occur at a return flow of 52C or below, so I'm trying to keep the rads as low as possible while still heating the house properly.
Question 1: I would like to measure the return flow myself to check on it - any tips on the most reliable way to do this? (The boiler itself doesn't appear to measure this.)
Question 2: What is the most likely reason for a high return flow temp? Rads that are too small?
All the piping and radiators on the system are new. Most are double panelled and double-finned Myson (or Myson-style) rads. There is a 1650x500 towel rail in the bathroom as well as an electric underfloor heating system.
Question 3: The towel rail manufacturer advertises its BTU for this model at Delta 70 (naughty I know). But at Delta 60 we were told it would offer 2,850 BTU's. I'm trying to get a sense of what BTU's we're actually getting from the rail given the way the system is operating.
My rough calculation = ((out+return/2)-room temp) = ((60+52/2)-19) = Delta 37. Yes or no? And if yes, does that mean the actual BTU is only 1750 or so?
Anyway, could someone help me understand this:
I have a new gas combi boiler, 30kw
When it was installed the plumber did a benchmark and noted down CH outflow temperature of 70C and return flow of 67C
This return flow seems too high to me. I currently have the CH outflow set to 60C as the manufacturer (Worcester Bosch) suggests condensing will only occur at a return flow of 52C or below, so I'm trying to keep the rads as low as possible while still heating the house properly.
Question 1: I would like to measure the return flow myself to check on it - any tips on the most reliable way to do this? (The boiler itself doesn't appear to measure this.)
Question 2: What is the most likely reason for a high return flow temp? Rads that are too small?
All the piping and radiators on the system are new. Most are double panelled and double-finned Myson (or Myson-style) rads. There is a 1650x500 towel rail in the bathroom as well as an electric underfloor heating system.
Question 3: The towel rail manufacturer advertises its BTU for this model at Delta 70 (naughty I know). But at Delta 60 we were told it would offer 2,850 BTU's. I'm trying to get a sense of what BTU's we're actually getting from the rail given the way the system is operating.
My rough calculation = ((out+return/2)-room temp) = ((60+52/2)-19) = Delta 37. Yes or no? And if yes, does that mean the actual BTU is only 1750 or so?