thanks for the post Eric, i can't touch anything yet, until I'm qualified , i will be looking at the NICEIC domestic installer scheme , and a job like this would be a great one for assessment when the time comes, ill keep you all in the loop
In the first era of general use of (30mA) RCDs (in TN installations), it was fairly common to just have a single 30mA RCD protecting all circuits in an installation, wasn't it? I lived with such an arrangement for many years, and at least a couple of members of my family still have such an arrangement.I had assumed with single RCD it would be 100mA specially since talking about TT with 30mA there is a problem should there be any faulty equipment working out what is faulty but that does not really cause a danger.
The OP's supply is very confusing- at least to me. There appear to be two DNO fuses, suggesting that there are two phases, but the OP says that there are only two overhead cables coming to his property. It therefore sounds as if a single phase feed for some reason splits somewhere before it gets to the fuses, which seems extremely odd. Furthermore, even if it were two phases, I've never heard of an E7 (or suchlike) supply utilising two phases - have you? Conversely, if it's single phase, it would seem very odd (and, again, definitely a new one on me) for the supply to split before two DNO fuses - have you ever seen that?As to two line supplies likely had economy 7 or similar at one point.

It is true that most people interpret the current regs as saying that operation of an RCD should not take out all of the circuits. However, what you describe would not achieve that. If there are any final circuits which are not protected by RCDs or RCBOs, then a fault on such a circuit will cause an up-front installation-wide RCD to operate (even if it is a 100mA time delayed one), hence taking out the entire installation. Similarly, a N-E fault on any final circuit will take out such an upfront 100mA RCD (hence whole installation) even if protected by a single-pole RCD or RCBO, since the single-pole device will not clear the N-E fault. The best solution (IMO) for a TT installation is to either have a dual-RCD (or 'high integrity') CU, with all final circuits protected by an RCD or RCBO, or to have an all-RCBO CU - in either case, you then don't need the up-front 100mA RCD.17th regs is that circuits need to be separately controlled so remaining circuits remain energised, says preferred arrangement is whole installation protected by 100ma RCD and install a split load protecting the sockets with a 30ma RCD....
It's probably worth talking to the DNO before you install an earth rod - it's just possible that, amidst that confusing supply, they could offer you a TN-C-S earth. Someone also needs to get to grips with what's actually going on with that supply!... ill check for an Earth Electrode and install one at the same time if not there, cheers guys for all the comments, as for the split from DNO thats what baffled me here
As you will have seen, that's something we've been speculating about. However, the OP says there are only two overhead (I assume 'single') cables supplying his property.I can't see anything else attached to the bottom service block, so is this unused phase?

You could call the DNO and say there is no earth on their incoming supply and ask for an engineer visit
Sure, but in this case it would be useful for the OP to know whether the DNO could/would supply an earth.As said many times the DNO is not obliged to provide an earth connection in this case. They might but it is at their descretion
there were 2 cables running from the street pylon to the house (i presume phase and neutral), then that ran into some partitioned external stud work and 3 cables on th either side, i could not get access to the external stud work so i guess the phase has just been split and the neutral ran solo, I'm assuming
Ah - but you only said that (slipped it in!) after I replied to what was originally the one-sentence post from youAs I said I'm not sure that the two connectors even contain fuses.
It seems that may well be the case.Reading this earlier post the OP needs to gain access to that area where I think a cut-out will be found
i was looking at the Kewtech KT65 or the Megger MFT1720 cheers peeps
Yep, that's certainly consistent with what westie suggested. You clearly need to try to find the cutout and see if there is any earth anywhere - like investigating that green wire! Good luck.