UFH Manifold Issues - Reverse flow?
sjn
15 Nov 2026
Hi all,
Looking for some advice on my UFH, which was installed during a renovation 2 years ago. It's never worked particularly well, taking hours to warm up and sometimes not reaching temperature at all on colder days.
It's a 4-loop system with a Wilo pump and mixing valve, sharing a boiler with the radiators.
I've been trying to figure out what's going on and noticed a few things:
- Flow meters show 1–2 L/min when the boiler fires, but gradually drop to zero when it stops, even though the UFH pump is still running and the thermostat is calling for heat.
- Increasing the pump power actually seems to reduce the flow, sometimes to zero. Switching to constant-pressure mode (setting 2) has helped a bit.
- Turning the mixing valve up to 60–65c gives me consistent flow, but dropping it back to 45c causes it to stop again. Obviously don't want to run it that hot with engineered wood flooring.
- The bottom manifold heats up before the top one (which has the flow meters). Shouldn't this be the other way around?
- It also seems to struggle more when the radiators are on.
The thing I'm most suspicious about is that the arrow on the Wilo pump points downwards, towards the bottom manifold.Is that correct for this setup? Could the water be circulating backwards through the manifold?
I'm wondering whether the boiler pump is doing most of the work, which might explain why the flow stops when the boiler stops firing, and why turning up the UFH pump seems to make things worse.
I spoke to an engineer who basically said that if the room eventually gets warm, he'd leave it alone. But it's been rubbish since installation and I'm worried something isn't right. Also don't want there be damage from incorrect flow.
Interested in people's thoughts. (I've watched about as much YouTube plumbing content as I can manage...)
Yes, the hot flow (to the manifolds) is from the bottom manifold, my daughter has the exact same set up (and pump), will poke out some info on outputs etc later, its working perfectly.
Interesting (/reassuring!) to know your daughter has a similar set up.
My understanding had been that the red limb with the flowmeters (top) is for flow, with the blue being the return.
If this is all plumbed correctly, I'm still not sure why the flow isn't constant when the thermostat is calling for heat, and why the higher pump speed seems to have a negative effect on flow rate.
Pump is installed the wrong way round, red is hot flow, blue is cold return from UFH. The UFH pump is opposing the main CH circ pump. Need to isolate and reverse that pump so it pushes the water up into the flow manifold.
What is controlling to flow to the floor? There are no valves on the return pipes, is there a two port valve somewhere on the feed to that manifold controlled by a stat in the kitchen?
Assuming the pump body hasn't been rotated on this image, you can see the OPs pump is installed in the opposite direction to a brochure image of the UFH manifold set up for the Wilo pump (ie the "O" in Wilo on the hot flow side), not the positioning on left or right of manifold.
Hi all,
Yes the daughters is different in that the TMV has a capillary (temperature measurement) and its some of the mixed flow water that returns to the boiler and not the "cold" from the UFH return, but it certainly works very well for the past 10 years or so, cant really comment on yours, strange though that there is a blue cold coloured isol valve before the TMV.
The head on the (daughters) Wilo pump was just turned through 180deg with the pump pumping downwards.
There should be labels on your TMV ports, what do they show?.
Thanks all for the replies.
I've added a wider view of the whole set up, and close up of the TMV, which I can only see one pipe labelled (R).
The pump is controlled by a stat in the Kitchen. The pump and boiler both fire up appropriately when the stat calls for heat.
The arrow on the back of the housing for the pump is pointing downwards (towards the TMV, away from the top bar) which seems like it's the wrong direction.